I have been wiring bar areas just as I do kitchens with 2 circuits on the counter top. Do I need to do that? Some one was telling me I do not and I asked the inspector and he never gave me a straight answer. If you have a article number that would be great thank you guys.
Todd
If there are no facillities for cooking food I don't believe this is a "kitchen". The only requirement is the GFCI assuming this is a "wet" bar. It could be served from a general lighting circuit IMHO. Certainly nobody will complain about having extra capacity but I doubt 4800va is justified.
A blender, a microwave, a lamp on the bar...who knows what else?
If you put in an outlet, the owner(comm. or home) will find something to plug into it!
~~ CELTIC ~~
...-= NJ =-...
The only reference to wet bar sinks is 210.8(A)(7).
I do not know of a reference in the NEC that even requires the wet bar counter to have receptacles, let alone having 2 circuits.
Branch circuits required - 210.11(C)
Receptacles required - 210.52
no mention of wet bars in these sections.
Pierre Belarge
e57 Offline
Of course there should be 2 circuits!