Joined: Mar 2005
Posts: 16
J
JoeMed Offline OP
Member
This installation has each phase double lugged to avoid double tapping the main service feeder breaker. From the service pedestal there is a 200amp service disconnect that feeds two 100amp panels, each is fed with 2/0 THHN (yes, a tad under) and both the 2/0 are lugged together one slightly longer to accommodate the breaker. To finish the installation, each of the wires go to a separate 100amp main breaker in a 100amp panel. Please advise was this an acceptable solution to this installation? Not my install. I have not seen this before.

Joined: Dec 2003
Posts: 524
Member
...Generally,(2)wires under one lug is a violation,unless that lug/breaker is listed for such..as far as I know,Square D,are the only breakers whose lugs are listed for (2)wires,..but 2/0?? how did they fit (2) of them under(1)lug?? sounds fishy to me...Good Luck!!
Russ

[This message has been edited by Attic Rat (edited 03-24-2005).]


.."if it ain't fixed,don't break it...call a Licensed Electrician"
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
I am not aware of any "box" lug (the ones with a hole in them) that is rated for multiple conductors per hole. Lugs with "pressure pads" are often rated for two conductors.

Joined: Jan 2005
Posts: 5,360
Likes: 1
Cat Servant
Member
Any electrical supply house has, or can get, a variety of devices to make this sort of connection properly.
One type has openings for three wires.....use with a short pigtail from the breaker.
The other is a machined block with connections for two wires, and a solid 'tail' that is inserted into the breaker.

Joined: Mar 2005
Posts: 16
J
JoeMed Offline OP
Member
thank you for the responses, I was n to clear on the lug. It is a double lug, with one wire in each lug, one wire longer to accommodate the breaker. Sound like it is not as bad as I thought?


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,722
Joined: October 2000
Top Posters(30 Days)
NORCAL 5
Trumpy 3
Popular Topics(Views)
300,303 Are you busy
229,981 Re: Forum
214,795 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5