0 members (),
153
guests, and
9
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Aug 2001
Posts: 545
OP
Member
|
Doing a job wiring an unattached residential garage. I have to run the 100 amp subpanel feeders through the attic then down the outside wall to a underground trench then to the garage. Would like to run 2/3 NM through the attic but then when I get to the UG trench, I don't want to have to change to #2 THHN just to go through the ridgid pipe underground, that will require a splice. Can I run the 2/3 NM through the ridgid pipe?. Or I could run #2 THHN through flex in the attic then convert to emt down the wall, then to ridgid underground. Any suggestions?
The Golden Rule - "The man with the gold makes the rule"
|
|
|
|
Joined: Jun 2004
Posts: 613
Member
|
Conduit underground is considered a wet location... Romex is not allowed in a wet location... Change over to pipe with thhn/thwn conductors...
shortcircuit
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
With an emphasis on th wn
|
|
|
|
Joined: Feb 2002
Posts: 375
Member
|
t is hard to find THHN that is not rated THWN
|
|
|
|
Joined: Oct 2004
Posts: 72
Member
|
|
|
|
|
Joined: Jul 2004
Posts: 9,932 Likes: 34
Member
|
I agree with bucketman. You could use smurf in the attic and LB into RNC when you go outside if running the pipe in the attic is a problem.
Greg Fretwell
|
|
|
|
Joined: Aug 2001
Posts: 545
OP
Member
|
Ya I agree, Prob the best way to go, I'll run pipe all the way. Thanks,
The Golden Rule - "The man with the gold makes the rule"
|
|
|
|
Joined: Jun 2004
Posts: 613
Member
|
aldav53...Jus noticed your in Arizona...gets real hot up there in those attics out there. Be sure to apply the ambient temperature correction factors for the wiring up in that there attic. You could use a correction factor that would cut the ampacity of the wiring by 50% Find this info below table 310.16 NEC... You would be better off to run underground to that garage. shortcircuit
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
"t is hard to find THHN that is not rated THWN"
Yes, As a matter of fact, I don't remember ever seeing any. You can bet, though, as soon as we say THHN is OK, that there will be some showing up for the first time. Accuracy is important, George
|
|
|
|
Joined: Aug 2001
Posts: 545
OP
Member
|
shortcircuit, Have to run through the attic then down to the trench. Yes it is hot in attics here. I may have to go larger than #2 for 100 amps.
The Golden Rule - "The man with the gold makes the rule"
|
|
|
Posts: 27