Subpanel - Garage - THHN/NM #49386
03/06/05 05:26 AM
03/06/05 05:26 AM
A
aldav53  Offline OP
Member
Joined: Aug 2001
Posts: 545
Chandler, AZ USA
Doing a job wiring an unattached residential garage. I have to run the 100 amp subpanel feeders through the attic then down the outside wall to a underground trench then to the garage. Would like to run 2/3 NM through the attic but then when I get to the UG trench, I don't want to have to change to #2 THHN just to go through the ridgid pipe underground, that will require a splice. Can I run the 2/3 NM through the ridgid pipe?. Or I could run #2 THHN through flex in the attic then convert to emt down the wall, then to ridgid underground.
Any suggestions?


The Golden Rule - "The man with the gold makes the rule"
Work Gear for Electricians and the Trades
Re: Subpanel - Garage - THHN/NM #49387
03/06/05 05:53 AM
03/06/05 05:53 AM
S
shortcircuit  Offline
Member
Joined: Jun 2004
Posts: 610
massachusetts
Conduit underground is considered a wet location...
Romex is not allowed in a wet location...
Change over to pipe with thhn/thwn conductors...

shortcircuit

Re: Subpanel - Garage - THHN/NM #49388
03/06/05 05:25 PM
03/06/05 05:25 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,280
Fullerton, CA USA
With an emphasis on thwn [Linked Image]

Re: Subpanel - Garage - THHN/NM #49389
03/06/05 10:24 PM
03/06/05 10:24 PM
G
George  Offline
Member
Joined: Feb 2002
Posts: 375
t is hard to find THHN that is not rated THWN

Re: Subpanel - Garage - THHN/NM #49390
03/06/05 10:59 PM
03/06/05 10:59 PM
B
bucketman  Offline
Member
Joined: Oct 2004
Posts: 72
vancouver WA, USA.
go pipe the hole way.

Re: Subpanel - Garage - THHN/NM #49391
03/07/05 12:51 AM
03/07/05 12:51 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,373
Estero,Fl,usa
I agree with bucketman. You could use smurf in the attic and LB into RNC when you go outside if running the pipe in the attic is a problem.


Greg Fretwell
Re: Subpanel - Garage - THHN/NM #49392
03/07/05 02:05 AM
03/07/05 02:05 AM
A
aldav53  Offline OP
Member
Joined: Aug 2001
Posts: 545
Chandler, AZ USA
Ya I agree, Prob the best way to go, I'll run pipe all the way.
Thanks,


The Golden Rule - "The man with the gold makes the rule"
Re: Subpanel - Garage - THHN/NM #49393
03/07/05 05:58 AM
03/07/05 05:58 AM
S
shortcircuit  Offline
Member
Joined: Jun 2004
Posts: 610
massachusetts
aldav53...Jus noticed your in Arizona...gets real hot up there in those attics out there.

Be sure to apply the ambient temperature correction factors for the wiring up in that there attic. You could use a correction factor that would cut the ampacity of the wiring by 50% [Linked Image]

Find this info below table 310.16 NEC...

You would be better off to run underground to that garage.

shortcircuit

Re: Subpanel - Garage - THHN/NM #49394
03/07/05 07:04 AM
03/07/05 07:04 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,280
Fullerton, CA USA
"t is hard to find THHN that is not rated THWN"

Yes, As a matter of fact, I don't remember ever seeing any. You can bet, though, as soon as we say THHN is OK, that there will be some showing up for the first time. Accuracy is important, George

Re: Subpanel - Garage - THHN/NM #49395
03/08/05 01:40 AM
03/08/05 01:40 AM
A
aldav53  Offline OP
Member
Joined: Aug 2001
Posts: 545
Chandler, AZ USA
shortcircuit,
Have to run through the attic then down to the trench. Yes it is hot in attics here. I may have to go larger than #2 for 100 amps.


The Golden Rule - "The man with the gold makes the rule"
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 362
Joined: April 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
257,129 Are you busy
192,961 Re: Forum
182,612 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.035s Queries: 15 (0.006s) Memory: 1.0236 MB (Peak: 1.1992 MB) Zlib enabled. Server Time: 2019-07-20 16:18:20 UTC