Doing a job wiring an unattached residential garage. I have to run the 100 amp subpanel feeders through the attic then down the outside wall to a underground trench then to the garage. Would like to run 2/3 NM through the attic but then when I get to the UG trench, I don't want to have to change to #2 THHN just to go through the ridgid pipe underground, that will require a splice. Can I run the 2/3 NM through the ridgid pipe?. Or I could run #2 THHN through flex in the attic then convert to emt down the wall, then to ridgid underground.
Any suggestions?


The Golden Rule - "The man with the gold makes the rule"
Joined: Jun 2004
Posts: 613
S
Member
Conduit underground is considered a wet location...
Romex is not allowed in a wet location...
Change over to pipe with thhn/thwn conductors...

shortcircuit

Joined: Dec 2000
Posts: 4,291
Member
With an emphasis on thwn [Linked Image]

Joined: Feb 2002
Posts: 375
G
Member
t is hard to find THHN that is not rated THWN

Joined: Oct 2004
Posts: 72
B
Member
go pipe the hole way.

Joined: Jul 2004
Posts: 9,788
Likes: 14
G
Member
I agree with bucketman. You could use smurf in the attic and LB into RNC when you go outside if running the pipe in the attic is a problem.


Greg Fretwell
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Ya I agree, Prob the best way to go, I'll run pipe all the way.
Thanks,


The Golden Rule - "The man with the gold makes the rule"
Joined: Jun 2004
Posts: 613
S
Member
aldav53...Jus noticed your in Arizona...gets real hot up there in those attics out there.

Be sure to apply the ambient temperature correction factors for the wiring up in that there attic. You could use a correction factor that would cut the ampacity of the wiring by 50% [Linked Image]

Find this info below table 310.16 NEC...

You would be better off to run underground to that garage.

shortcircuit

Joined: Dec 2000
Posts: 4,291
Member
"t is hard to find THHN that is not rated THWN"

Yes, As a matter of fact, I don't remember ever seeing any. You can bet, though, as soon as we say THHN is OK, that there will be some showing up for the first time. Accuracy is important, George

Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
shortcircuit,
Have to run through the attic then down to the trench. Yes it is hot in attics here. I may have to go larger than #2 for 100 amps.


The Golden Rule - "The man with the gold makes the rule"
Page 1 of 2 1 2

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Top Posters(30 Days)
BigB 9
triple 3
Popular Topics(Views)
302,374 Are you busy
231,775 Re: Forum
216,398 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5