ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (CoolWill), 250 guests, and 13 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#49337 03/04/05 08:57 PM
Joined: Aug 2004
Posts: 186
N
Member
Ok i think i am ready to flip out over this topic, i have had it out with more people over the proper responce to the following?

looking to find out the proper size wires for the below listed services as well as the proper size wire to ground rod and wire to water pipe. I have been arguing this on out way to ften lately so lets see what everyone out goes with. if poss code ref. #'s would be great i go with 310.15(B)(6) myself

Services;
100 amp = wire size cooper & alum.
150 amp= same
200 amp= same

as well as bonding for each.
and ground to ground rods for each.

#49338 03/04/05 09:13 PM
Joined: May 2004
Posts: 162
C
Member
dwellings??

#49339 03/04/05 09:32 PM
Joined: Aug 2004
Posts: 186
N
Member
yes resi. work,
not commercial

#49340 03/04/05 09:33 PM
Joined: Jan 2002
Posts: 163
D
Member
IF you are sizing for dwelling units, then 310.15(B)(6) is the correct table to determine service conductor sizes.

You say grounding electrode conductors to ground rods - 250.66(A) says #6 copper to the rod regardless of the service size.

Bonding?...bonding what?

Main Bonding Jumper? 250.28(D) says to use Table 250.66 and size your jumper based on the size of the service conductor

Bonding to water pipe (dwelling water service) - 250.66 says to use Table 250.66

Bonding jumper used to connect grounding electrodes together to form the grounding electrode system - 250.53(C) says to size per 250.66

Bonding metal water piping systems installed in or attached to a building - 250.104(A)(1) says to size in accordance with Table 250.66