#49337 03/04/05 08:57 PM
Joined: Aug 2004
Posts: 186
N
Member
Ok i think i am ready to flip out over this topic, i have had it out with more people over the proper responce to the following?

looking to find out the proper size wires for the below listed services as well as the proper size wire to ground rod and wire to water pipe. I have been arguing this on out way to ften lately so lets see what everyone out goes with. if poss code ref. #'s would be great i go with 310.15(B)(6) myself

Services;
100 amp = wire size cooper & alum.
150 amp= same
200 amp= same

as well as bonding for each.
and ground to ground rods for each.

Horizontal Ad
#49338 03/04/05 09:13 PM
Joined: May 2004
Posts: 162
C
Member
dwellings??

#49339 03/04/05 09:32 PM
Joined: Aug 2004
Posts: 186
N
Member
yes resi. work,
not commercial

#49340 03/04/05 09:33 PM
Joined: Jan 2002
Posts: 163
D
Member
IF you are sizing for dwelling units, then 310.15(B)(6) is the correct table to determine service conductor sizes.

You say grounding electrode conductors to ground rods - 250.66(A) says #6 copper to the rod regardless of the service size.

Bonding?...bonding what?

Main Bonding Jumper? 250.28(D) says to use Table 250.66 and size your jumper based on the size of the service conductor

Bonding to water pipe (dwelling water service) - 250.66 says to use Table 250.66

Bonding jumper used to connect grounding electrodes together to form the grounding electrode system - 250.53(C) says to size per 250.66

Bonding metal water piping systems installed in or attached to a building - 250.104(A)(1) says to size in accordance with Table 250.66

#49341 03/04/05 11:03 PM
Joined: Aug 2004
Posts: 186
N
Member
kicking this back up top again


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Top Posters(30 Days)
BigB 6
timmp 2
Popular Topics(Views)
329,530 Are you busy
254,376 Re: Forum
236,838 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5