ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 516 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#48381 02/10/05 10:51 AM
Joined: Jun 2002
Posts: 206
H
Member
Is there any code against running a 100 AMP Sub Panel off of a 150 AMP Main Breaker Panel? Its a residential application the person who initially tlooked at the job mistook it for a 200 AMP Main and bid for a 100 AMP Sub. Just trying to save the checkbook to avoids eating a 200 AMP upgrade...

Any help?

Joined: Jan 2003
Posts: 4,391
I
Moderator
Sure, you could connect a 200 amp rated subpanel onto a 100 amp service panel if you wanted to.

There is only one issue to consider and that is the total calculated load or the real demand load for the past year.

So if either the calculated load or the demand load is under 150 amps you are good to go.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Nov 2004
Posts: 80
B
Member
I don't believe there would be a problem as long as you size your conductors accordingly. I'm assumming that your 100 amp panel is a main lug only. If this were the case then your protection and means of disconnection is back at your 150amp panel. I would check with your local inspector, it may fall into an issue on that level.

Best of luck!!!

Joined: Apr 2002
Posts: 914
E
Member
You could have a 100 amp sub off of a 100 amp sub off a 100 amp sub off a 100 amp sub off a 150 amp main. In other words your OK most likely.

Joined: Jun 2002
Posts: 206
H
Member
Right on. Then 100 AMP Sub'd we be.