#48317 02/09/05 11:22 AM
Joined: Feb 2005
Posts: 1
J
Junior Member
Can you properly splice 6 or 8 #12 under a grey wire nut. I have had nothing but problems with splice coming apart.

#48318 02/09/05 11:38 AM
Joined: May 2002
Posts: 1,716
R
Member
You can splice up to (6) #12's, go to the link below for one manufacturers info.

click on the "Wing Twist" type
http://www.idealindustries.com/wt/TwistOnWireConnectors.nsf

Roger

[This message has been edited by Roger (edited 02-09-2005).]

#48319 02/09/05 01:34 PM
Joined: May 2004
Posts: 697
D
Member
Try stripping all the wires, lining them up together and wrapping tape tightly around them near the end. This keeps them all lined up. It's easier if you're using stranded wire. If it still gives you trouble, use a split bolt.

Dave

#48320 02/09/05 01:47 PM
Joined: Dec 2003
Posts: 886
H
Member
People usually have problems because the conductors are too short to hold and/or the stripped ends are not lined up or long enough.

When I do this I strip a little more than what is needed, line them all up, pre-twist, then cut the end off to the proper length. Never had a problem with even more than 6 or 8 #12s and the proper wire nut.

-Hal

#48321 02/09/05 02:24 PM
Joined: Jul 2002
Posts: 717
M
Member
I have never been a great fan of that many wires under one wirenut whether it is a gray or a big blue. My work around in those same situations is to make what I call a bridge splice. Its simple - four of the wires under one wire nut and four of the wires under another wire nut with a jumper from one wirenut to the other one. Granted you will use an extra gray wirenut, but for me its peace of mind. Or go with the split bolt as has been said. Those cost $6 bucks for the #2 size here nowadays.

#48322 02/09/05 02:57 PM
Joined: Dec 2003
Posts: 751
E
Member
If you go with the split-bolt you run the risk of a red tag. Split bolts are listed for 2 conductors only.


Earl
#48323 02/09/05 03:36 PM
Joined: Jul 2004
Posts: 625
S
Member
I recall reading that, in Europe, they have splicing devices that consist of an insulated bar with individual holes to recieve each wire, and a compression screw for each wire. Very neat, and very secure connections. Is anything like that available in the US?

[This message has been edited by SolarPowered (edited 02-09-2005).]

#48324 02/09/05 04:00 PM
Joined: Sep 2003
Posts: 650
W
Member
There are various block of this sort available in the US, eg:
http://www.polarisconnectors.com/index.html

I don't know if there are _smaller_ size versions available, but the large ones are a great replacement for split bolts.

-Jon

#48325 02/09/05 05:24 PM
Joined: Jul 2004
Posts: 625
S
Member
That's exactly the sort of thing I was thinking of. The smallest one they have is for #4-14, so it's really huge for splicing #12.

Is there anything smaller around?

#48326 02/09/05 05:53 PM
Joined: Aug 2004
Posts: 34
H
Member
If your look at any container that wire nuts came in they have a chart on the side. I have never seen on any of those charts show you can put more than 5 wires under a single connector. I believe method of shoving all these wires under one wire nut is poor. This must be a heck of a big juction box.