#47194 01/11/05 08:16 PM
Joined: Jan 2005
Posts: 53
D
Member
any comments on connections to outside skid mount pump on classification and wiring methods?

Thanx Denny

Horizontal Ad
#47195 01/12/05 08:15 AM
Joined: Nov 2000
Posts: 2,148
R
Member
Denny,
Diesel fuel is not a flammable liquid (it is combustible) and the diesel fuel handling area is not a classified area.
Don


Don(resqcapt19)
#47196 01/12/05 09:05 AM
Joined: Nov 2004
Posts: 56
D
Member
just installed one. inspector told us to explosion proof everything within 10' of the tank all the way around. if it would have been gasoline it would have been a bigger radius.


Scott
#47197 01/12/05 09:07 AM
Joined: Mar 2003
Posts: 849
Y
Member
Denny
You have to make sure the conduit or conduits feeding the Diesel Skid do not pass thur a classified area. If they do then they require to be treated as classified . This is done a lot where theres both Gas and Diesel pumps in the same area.

#47198 01/12/05 10:46 AM
Joined: Aug 2001
Posts: 7,520
P
Member
Quote
Diesel fuel is not a flammable liquid
Indeed. I have a friend who is a retired trucker and he tells of the time that some manager at a depot balled at him to put a cigarette out while he was pumping diesel into the truck.

He said he just threw the butt into the diesel tank and you've never seen somebody run for cover so fast! Guess he proved the point though! [Linked Image]

#47199 01/12/05 11:52 AM
Joined: Nov 2000
Posts: 2,148
R
Member
Quote
514.3 Classification of Locations.
(A) Unclassified Locations. Where the authority having jurisdiction can satisfactorily determine that flammable liquids having a flash point below 38°C (100°F), such as gasoline, will not be handled, such location shall not be required to be classified.
Diesel has a flash point above 100°F and therefore the area is not required to be classified.
Don


Don(resqcapt19)
#47200 01/12/05 11:55 AM
Joined: Nov 2000
Posts: 2,148
R
Member
Quote
You have to make sure the conduit or conduits feeding the Diesel Skid do not pass thur a classified area. If they do then they require to be treated as classified .
That would only require that the conduits have seals at the boundries. It would not require the use of explosionproof wiring methods at the diesel dispensing area.
Don


Don(resqcapt19)
Horizontal Ad
#47201 01/12/05 03:14 PM
Joined: Jul 2002
Posts: 680
W
Member
Quote
That would only require that the conduits have seals at the boundries. It would not require the use of explosionproof wiring methods at the diesel dispensing area.
This is true although if on the same concrete island as a gas pump I treat them the same no matter the distance apart.
Fuel oil generally has a flash point above 125 f I believe.

#47202 01/12/05 03:34 PM
Joined: Jan 2005
Posts: 53
D
Member
Thanks for the quick response guys....


This was my first post on this site !!

I used to watch the forum that R Keis has but there is so much more info on this one and seems less bickering too... Again thanks..

#47203 01/12/05 09:18 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Quote
This is true although if on the same concrete island as a gas pump I treat them the same no matter the distance apart.
If they are close to each other the diesel dispenser may fall within the classified area for the gas dispenser and if so, then the electrical equipment within the classified area must meet the classification.
Don


Don(resqcapt19)

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Top Posters(30 Days)
Popular Topics(Views)
363,487 Are you busy
286,303 Re: Forum
264,840 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5