Electricians revenge
0 members (), 46 guests, and 9 robots.
Shortcircuit, Shane is correct.
Go to this Southwire page and scroll dow to NM-B for an explanation.
Roger
Its been so long since I learned why I run #8 romex to ranges that I forgot about 220.19
The demand factor of 1 range of 12kw is 8kw and thats why I run #8 to my ranges.Which code rule allows that #8 to be on a 50 amp breaker?
shortcircuit
I do not understand.
310.16 rates 8 AWG copper 50 amps at 75 C
As long as we are not using NM and the wire, breaker and other terminals are all 75 C listed we can use a 50 amp breaker with 8 AWG copper.
NM is different regardless of the THHN inside it.
334.80 Ampacity.
The ampacity of Types NM, NMC, and NMS cable shall be determined in accordance with 310.15. The ampacity shall be in accordance with the 60°C (140°F) conductor temperature rating. The 90°C (194°F) rating shall be permitted to be used for ampacity derating purposes, provided the final derated ampacity does not exceed that for a 60°C (140°F) rated conductor. The ampacity of Types NM, NMC, and NMS cable installed in cable tray shall be determined in accordance with 392.11.
iwire...every freestanding range I've wired for the last 25 years has been wired with # 6 aluminum or # 8 copper connected to a 50 amp breaker.Thats what I was taught to use and thats the way I see electric ranges connected.I used to use #6 SEU until we had to use 4 wire and then I switched to 8-3 romex and I have never been sited for a violation.?
shortcircuit
Shortcircuit, in the case of "I used to use #6 SEU (AL per above) until we had to use 4 wire and then I switched to 8-3 romex and I have never been cited for a violation". The inspectors simply have not spotted the violation.
Inspectors are like Inspectees, they both make mistakes. [Linked Image]
Roger
[This message has been edited by Roger (edited 01-13-2005).]
So 8-3 romex protected with a 50 Amp breaker for a Range (up to 12KW) is a violation, but can you wire the range with 8-3 romex and use a 40Amp braeaker per Table 220.19 Note 4:
Table 220.19 Note 4. Branch-Circuit Load. It shall be permissible to compute the branch circuit load for one range in accordance with Table 220.19.
Per Table 220.19 Column C:
compute branch circuit load at 8KW
8KW/220V=36.33Amps
8-3 romex with 40Amp breaker OK?
Iwire,Electric Ian,
A quote from the 2002 Massachusetts Electric code:
"334.80. Revise to read as follows:
334.80 Ampacity. Type NM, NMC, and NMS cable shall have conductors rated at 90C(194F). Where installed in thermal insulation, the ampacity of conductors shall be that of 60C(140F) conductors. The ampacity of Types NM, NMC,and NMS cable installed in cable trayshall be determined in accordance with 392.11."
This revision seems to allow #8-3 copper romex to be protected by a 50 amp breaker where the wire isn't installed in insulation...here in Massachusetts.
shortcircuit
I agree and that is a good point for us MA folks.
Bob
shortcircuit ---
It is not clear if the ampacity is before or after final derating.
The intent of the code could be to derate from the 60 degree colume within insulated walls.
George...It is my understanding, for derating purposes the 90C column is used.A 8-3 romex cable run by itself needs no derating.
I interpet the MA code (334.80) that I posted to mean if the 8-3 copper romex I run in a dwelling is imbeded in thermal insulation that I must use the 60C column which restricts the wire to 40amps.
If the wire is run through the basement(which most houses in New England have)along the sill and up through the floor to the freestanding range, NOT imbeded in thermal insulation, then the wire will be good for 50 amps as listed in the 75C column in 310.16
Also take note of the temperature correction factor table below 310.16. If the wire is run in the basement where the average tempature will be 70F-77F or lower around here, I can apply a correction factor of 1.05...or 50amps x 1.05= 52.5amps
On the other hand if the wire is run up through the ceiling embeded in thermal insulation exposed to attic tempatures in excess of (lets say) 114F-122F, then I would figure the amperage of that #8 copper romex from the 60C column with a tempature correction factor of .58...40amps x .58= 23.2 amps.
Quite a swing in allowable ampacity [Linked Image]
shortcircuit