Electricians revenge
1 members (Scott35), 25 guests, and 12 robots.
#46298 12/19/04 06:01 PM
Sparks what is the secondary voltage you are looking for?
Al
#46299 12/19/04 06:11 PM
Al he wants to go from 208 to 240 volt.
Bob
#46300 12/19/04 06:16 PM
mxslick
Cap off x2; not used here
No that is not right all conductors will be used.
Look at Scott35's post with the schematic, that is the connection.
#46301 12/19/04 07:00 PM
Bob:
You're right if his transformer has an x4 connection, what he posted leaves the impression that his secondary has only three wires brought out. That made me pause too when composing my reply. If he has 4 wires on secondary, then scott35's schematic is the ticket. [Linked Image]
If his transformer has only x1,x2,x3 brought out, then the x2/x3 connection is a short (in the connections he described in the post abvove mine) and will release smoke. [Linked Image]
Sparks30, tell the masses what your wires are! [Linked Image] We're on the edge of our seats!
Edit: If he does indeed have an x4, then it should go like this:
Wire H1 to one leg of 208;
Nut H2 AND x1 together, this is the other leg of 208;
Nut x2 and x3; LOAD will connect as :
One leg to H1;
Other leg to x4
I need an aspirin. [Linked Image]
[This message has been edited by mxslick (edited 12-19-2004).]
Stupid should be painful.
#46302 12/20/04 11:34 PM
mxslick you're on the money. You got the config. Also to find out we were supplied the wrong trany. Thanks everyone
