Posted By: Sparks30 Buck Boost - 12/18/04 03:27 PM
Has anyone installed a 208 to 40 buck boost. I intalled a Ge the wiring said to attach the line side to the h1 and h2 and line to x1 and x2 and wire nut x2 and x3. Well the trans smoked. does the config seem right. Thanks
Posted By: Bjarney Re: Buck Boost - 12/18/04 10:29 PM
 
See www.federalpacific.com/literature/drytrans/FPTS-RTB-0701.pdf possibly “figure B” on page 40.. There are plenty of variations—judge for yourself.
Posted By: Sparks30 Re: Buck Boost - 12/19/04 02:38 AM
The trans I had only had a H! and H2. Do these get tied to line or load. It is like pg 42 diagram 2
Posted By: Crowbar Re: Buck Boost - 12/19/04 03:38 AM
Your connections do not sound correct, can you post the xfmr data or connection information that was supplied? Perhaps we can decipher better then.
Posted By: Scott35 Re: Buck Boost - 12/19/04 01:43 PM
Looks like you have a 240 VAC × 16/32 VAC Split Coil (Secondary) 1Ø Isolated Transformer - judging from the Voltages listed and the Terminals
(Input = 208 VAC, Output = 240 VAC - hence the 32 VAC Secondary, + H1, H2, X1, X2, X3, X4).

Take a look at these Schematics from the Technical Reference Section:

[Linked Image]
Image #1: Pictorial View

[Linked Image]
Image #2: 1 Line View

Actually, the Voltages listed in these Schematics differ from yours, but the concepts are the same.
Along with this, instead of having a Split Coil Primary, or a Primary setup for use at either 120 or 240 VAC as these drawings show, your Transformer has a Single Primary Coil wound for 240 VAC (or 208 VAC).

The Terminals on your Xformer would be "H1" and "H2" only, so in this case, your Transformer would have the "H2" Termination done to where the "H4" Termination is shown in the Schematics.
This way, the Secondary Coils are in a Series Adding Connection methodology...

FYI, refer to the Tech. Reference section for more drawings and details, regarding the Voltage Boosting and Voltage Bucking setups.

Let us know if you do not understand this information, and if the Transformer is salvagable,
or you are able to Put The Smoke Back Inside The Windings
[Linked Image]

Scott35
Posted By: Sparks30 Re: Buck Boost - 12/19/04 02:34 PM
I do not have the specs. I ws talking to a friend and he said the ame thing about not sounding right. When I get the newone monday I will try to post them. thanks for the help.
Posted By: capt al Re: Buck Boost - 12/19/04 03:43 PM
Sparks, take a look at page 44 diagram 10A. It looks more like what you are trying to do.
Al
Posted By: Sparks30 Re: Buck Boost - 12/19/04 05:28 PM
I tied H1 to 1leg of input208 and H2 to other leg of input. Then wire nuted the x2-x3 together. Then 1leg of output to x1 and the other leg to x2.
Posted By: mxslick Re: Buck Boost - 12/19/04 09:03 PM
Sparks; from what you just posted sounds ilke you've connected the primary correctly, but the x2/x3 connection shorted half of the secondary winding. The connection from primary to secondary as in the diagrams was missing from your hookup. So:

Wire H1 to one leg of 208;
Nut H2 AND x1 together, this is the other leg of 208;
Cap off x2; not used here
LOAD will connect as :
One leg to H1;
Other leg to x3

That should do it. Comments, gentlemen?
Posted By: Sparks30 Re: Buck Boost - 12/19/04 09:43 PM
That sound more like it. The trans came out of the box with no paperwork, so I had to go with what was on the trans itself. everyone thanks for the help. I'll try not to smoke onother one.
Posted By: capt al Re: Buck Boost - 12/19/04 10:01 PM
Sparks what is the secondary voltage you are looking for?
Al
Posted By: iwire Re: Buck Boost - 12/19/04 10:11 PM
Al he wants to go from 208 to 240 volt.

Bob
Posted By: iwire Re: Buck Boost - 12/19/04 10:16 PM
mxslick

Quote
Cap off x2; not used here

No that is not right all conductors will be used.

Look at Scott35's post with the schematic, that is the connection.
Posted By: mxslick Re: Buck Boost - 12/19/04 11:00 PM
Bob:

You're right if his transformer has an x4 connection, what he posted leaves the impression that his secondary has only three wires brought out. That made me pause too when composing my reply. If he has 4 wires on secondary, then scott35's schematic is the ticket. [Linked Image]

If his transformer has only x1,x2,x3 brought out, then the x2/x3 connection is a short (in the connections he described in the post abvove mine) and will release smoke. [Linked Image]

Sparks30, tell the masses what your wires are! [Linked Image] We're on the edge of our seats!

Edit: If he does indeed have an x4, then it should go like this:

Wire H1 to one leg of 208;
Nut H2 AND x1 together, this is the other leg of 208;
Nut x2 and x3; LOAD will connect as :
One leg to H1;
Other leg to x4

I need an aspirin. [Linked Image]



[This message has been edited by mxslick (edited 12-19-2004).]
Posted By: Sparks30 Re: Buck Boost - 12/21/04 03:34 AM
mxslick you're on the money. You got the config. Also to find out we were supplied the wrong trany. Thanks everyone