ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
GFCI's pops in large numbers
by dsk - 09/26/22 04:35 AM
AFCI’s Revisited
by sparky - 09/24/22 09:58 AM
NFPA Price Increase Coming
by Bill Addiss - 09/23/22 02:22 PM
Siemens breakers
by gfretwell - 09/23/22 01:45 PM
What do you look like?II
by HotLine1 - 09/22/22 12:33 PM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
0 members (), 26 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#45828 12/07/04 07:28 PM
Joined: Mar 2002
Posts: 179
D
derater Offline OP
Member
Home where the h/o was messing w/ his dryer and (likely) shorted power to frame; then got bright/dim condition usually blamed on bad noodle; they all looked ok though it's a 50 y/o system w/ lots of stuff bundled, etc.
In the meter base at 1 hot lug was nasty rusted screw head.Line side had no votage difference, but with meter in it avg.150/90, at panel.
At any rate the whole affair is a mess (no
main breaker, split buss (?) Zinsco.Am doing 100/200a upgrade, now praying it's balanced.
Thoughts?

#45829 12/07/04 09:17 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
I'm thinking that the problem was a loose neutral, it could be anywhere between the panel & the transformer.

I ran across a Zinsco panel a couple of weeks ago on an inspection. i thought after I moved back East, I'd be lucky & never see one again, but I was mistaken. They are the FPE of the West.

Tom


Few things are harder to put up with than the annoyance of a good example.
#45830 12/07/04 11:20 PM
Joined: Sep 2002
Posts: 924
Likes: 1
N
Member
Zinsco is Los Angeles'contribution to the electrical world. [Linked Image]

#45831 12/08/04 10:46 AM
Joined: Mar 2004
Posts: 76
M
Member
It is a neutral problem...Something I have done is to eliminate the Customers equipment, by taking a piece of #4 thhn & split bolt it onto the POCO's service neutral, & connect it to the panel's neutral bar.
If the inbalance is still there, it will be a problem with the POCO's neutral connections.
If the inbalance straightens itself out, the hunt begins !!! but You will know that it is inside the Customers equipment.
The last time I did this trick, I found the problem went away, & voltage was good.
Called the POCO & told them THEY had a open neutral.....found out that a Squirrel had chewed the neutral down to the steel core out on the pole.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,289
Joined: December 2000
Top Posters(30 Days)
dsk 3
Popular Topics(Views)
297,409 Are you busy
228,264 Re: Forum
213,161 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5