volt difference at panel #45828
12/07/04 07:28 PM
12/07/04 07:28 PM
D
derater  Offline OP
Member
Joined: Mar 2002
Posts: 179
Home where the h/o was messing w/ his dryer and (likely) shorted power to frame; then got bright/dim condition usually blamed on bad noodle; they all looked ok though it's a 50 y/o system w/ lots of stuff bundled, etc.
In the meter base at 1 hot lug was nasty rusted screw head.Line side had no votage difference, but with meter in it avg.150/90, at panel.
At any rate the whole affair is a mess (no
main breaker, split buss (?) Zinsco.Am doing 100/200a upgrade, now praying it's balanced.
Thoughts?

Work Gear for Electricians and the Trades
Re: volt difference at panel #45829
12/07/04 09:17 PM
12/07/04 09:17 PM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
I'm thinking that the problem was a loose neutral, it could be anywhere between the panel & the transformer.

I ran across a Zinsco panel a couple of weeks ago on an inspection. i thought after I moved back East, I'd be lucky & never see one again, but I was mistaken. They are the FPE of the West.

Tom


Few things are harder to put up with than the annoyance of a good example.
Re: volt difference at panel #45830
12/07/04 11:20 PM
12/07/04 11:20 PM
N
NORCAL  Offline
Member
Joined: Sep 2002
Posts: 882
Zinsco is Los Angeles'contribution to the electrical world. [Linked Image]

Re: volt difference at panel #45831
12/08/04 10:46 AM
12/08/04 10:46 AM
M
Megawatt  Offline
Member
Joined: Mar 2004
Posts: 76
Lexington,Ky, USA
It is a neutral problem...Something I have done is to eliminate the Customers equipment, by taking a piece of #4 thhn & split bolt it onto the POCO's service neutral, & connect it to the panel's neutral bar.
If the inbalance is still there, it will be a problem with the POCO's neutral connections.
If the inbalance straightens itself out, the hunt begins !!! but You will know that it is inside the Customers equipment.
The last time I did this trick, I found the problem went away, & voltage was good.
Called the POCO & told them THEY had a open neutral.....found out that a Squirrel had chewed the neutral down to the steel core out on the pole.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,546 Are you busy
190,777 Re: Forum
180,501 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 14 (0.004s) Memory: 0.9595 MB (Peak: 1.0914 MB) Zlib enabled. Server Time: 2019-04-23 22:07:33 UTC