Joined: May 2003
Posts: 2,876
OP
Member
|
Any of our many California gent's out there know if ADA heights have changed? ie. 18"CL and 42"CL AFF Second time recently that I have gotten plans requesting 15, and 48".
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Mark, does California have its own ADA codes?
Roger
|
|
|
|
Joined: May 2003
Posts: 2,876
OP
Member
|
Yep.... Not sure if has changed or not?
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Well, none of the heights you give are all inclusive of true ADA codes.
For side access the minimum is 9" and the maximum is 54"
Roger
[This message has been edited by Roger (edited 10-15-2004).]
|
|
|
|
Joined: Apr 2002
Posts: 558
Member
|
15" minimum and 48" maximum is what I have always seen in the specs.
Curt
Curt Swartz
|
|
|
|
Joined: Dec 2000
Posts: 4,293
Member
|
I understand it to be as Curt says. +15, +48.
|
|
|
|
Joined: May 2003
Posts: 2,876
OP
Member
|
Wow, for years, and it's not just me, several people I have worked for too, but around here we have been doing >18", and <42", as an ADA thing. Not that any of us wants to go get a book for $60+ bucks to just to find out plug and switch hieghts on a half page. And have a book that also contains how much turning radius area is needed in a toilet, and everything else too.
Anyway, thanks gents.
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Here you go Mark, Figure 5a High Forward Reach Limit Forward reach range shown in profile and plan view to be 48 inches maximum and 15 inches minimum. Figure 5b Maximum Forward Reach over an Obstruction The maximum level forward reach over an obstruction with knee space below is 25 inches (635 mm). When the obstruction is less than 20 inches (510 mm) deep, the maximum high forward reach is 48 inches (1220 mm). When the obstruction projects 20 to 25 inches (510 mm to 635 mm), the maximum high forward reach is 44 inches (1120 mm). (4.2.5, 4.25.3). Figure 6(b) High and Low - Side Reach Limits The 30 by 48 inch wheelchair clear floor space is located a maximum 10 inches (255 mm) from the wall. Roger [This message has been edited by Roger (edited 10-16-2004).]
|
|
|
|
Joined: May 2003
Posts: 2,876
OP
Member
|
Once again a thanks to you, I did how-ever go on down to the library to confirm this. (As I was kicked out of the house for a bridal shower, and it's rainy day.) But from what I make of this, is that the minimum and maximum are determined by approach. So >15" to bottom of the receptical, and <48" to top of the switch would seem be the way to go, as something like this could easily be over-enforced. Better safe than sorry, or conservitive rather than costly.
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: May 2003
Posts: 2,876
OP
Member
|
Roger, Seems you have the book, and..... Dare I say it could I get one more from ya? Please. Side reach over obstical, like a kitchen counter.
I would really appreciate it.
Thank you in advance.
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|