Posted By: e57 Cali ADA plug and switch hieghts? - 10/15/04 10:46 PM
Any of our many California gent's out there know if ADA heights have changed? ie. 18"CL and 42"CL AFF Second time recently that I have gotten plans requesting 15, and 48".
Posted By: Roger Re: Cali ADA plug and switch hieghts? - 10/15/04 11:33 PM
Mark, does California have its own ADA codes?

Roger
Posted By: e57 Re: Cali ADA plug and switch hieghts? - 10/16/04 12:05 AM
Yep.... Not sure if has changed or not?
Posted By: Roger Re: Cali ADA plug and switch hieghts? - 10/16/04 12:13 AM
Well, none of the heights you give are all inclusive of true ADA codes.

For side access the minimum is 9" and the maximum is 54"

Roger

[This message has been edited by Roger (edited 10-15-2004).]
Posted By: caselec Re: Cali ADA plug and switch hieghts? - 10/16/04 12:47 AM
15" minimum and 48" maximum is what I have always seen in the specs.

Curt
Posted By: electure Re: Cali ADA plug and switch hieghts? - 10/16/04 11:40 AM
I understand it to be as Curt says. +15, +48.
Posted By: e57 Re: Cali ADA plug and switch hieghts? - 10/16/04 04:53 PM
Wow, for years, and it's not just me, several people I have worked for too, but around here we have been doing >18", and <42", as an ADA thing. Not that any of us wants to go get a book for $60+ bucks to just to find out plug and switch hieghts on a half page. And have a book that also contains how much turning radius area is needed in a toilet, and everything else too.

Anyway, thanks gents.
Posted By: Roger Re: Cali ADA plug and switch hieghts? - 10/16/04 09:57 PM
Here you go Mark,

[Linked Image from access-board.gov]

Figure 5a
High Forward Reach Limit


Forward reach range shown in profile and plan view to be 48 inches maximum and 15 inches minimum.

[Linked Image from access-board.gov]

Figure 5b
Maximum Forward Reach over an Obstruction


The maximum level forward reach over an obstruction with knee space below is 25 inches (635 mm). When the obstruction is less than 20 inches (510 mm) deep, the maximum high forward reach is 48 inches (1220 mm). When the obstruction projects 20 to 25 inches (510 mm to 635 mm), the maximum high forward reach is 44 inches (1120 mm). (4.2.5, 4.25.3).


[Linked Image from access-board.gov]

Figure 6(b)
High and Low - Side Reach Limits


The 30 by 48 inch wheelchair clear floor space is located a maximum 10 inches (255 mm) from the wall.


Roger



[This message has been edited by Roger (edited 10-16-2004).]
Posted By: e57 Re: Cali ADA plug and switch hieghts? - 10/18/04 01:37 AM
Once again a thanks to you, I did how-ever go on down to the library to confirm this. (As I was kicked out of the house for a bridal shower, and it's rainy day.) But from what I make of this, is that the minimum and maximum are determined by approach. So >15" to bottom of the receptical, and <48" to top of the switch would seem be the way to go, as something like this could easily be over-enforced. Better safe than sorry, or conservitive rather than costly.
Posted By: e57 Re: Cali ADA plug and switch hieghts? - 10/28/04 12:05 AM
Roger, Seems you have the book, and..... Dare I say it could I get one more from ya? Please. Side reach over obstical, like a kitchen counter.

I would really appreciate it.

Thank you in advance.
Posted By: Roger Re: Cali ADA plug and switch hieghts? - 10/28/04 12:28 AM
Mark, ask and ye shall receive. [Linked Image]

[Linked Image from access-board.gov]

Figure 6(c)
Maximum Side Reach over Obstruction


If the depth of the obstruction is 24 inches (610 mm) and the maximum height of the obstruction is 34 inches (865 mm), the maximum high side reach over the obstruction is 46 inches (1170).

Mark you can access this info below.

Click Here for the ADA

Roger
Posted By: Admin Re: Cali ADA plug and switch hieghts? - 10/28/04 01:29 AM
Moved to Building Codes Area:
https://www.electrical-contractor.net/ubb/Forum18/HTML/000078.html