Hi,
What do you charge for a 100 or 200A service installed at a single family dwelling? Does not include PERMIT.
Here is a material list and what I charge:
Equipment is GE.
100A - $750
1 Weatherhead (5 hole) 1 1/2"
15' Conduit (IMC) 1 1/2"
1 Meter base 100 Amp
1 Nipple (2 1/2" to 4" long)1 1/2"
2 Locknuts 1 1/2"
1 Plastic Bushing 1 1/2"
1 Main breaker 100 Amp
1 Weatherproof breaker box 100 Amp
1 Hub for above breaker box 1 1/2"
22' Neutral Conductor #6 AWG
86' #2 THW Conductor (copper)for line and load side
4 Conduit straps & screws 1 1/2"
4 Lag screws 3/8" X 3"
1 Roof Flashing 2-1/2"
200A $1100
1 Weatherhead (5 hole) 2 1/2"
15' Conduit (IMC) 2 1/2"
1 Meter base 200 Amp
1 Nipple (2 1/2" to 4" long)2 1/2"
2 Locknuts 2 1/2"
1 Plastic Bushing 2 1/2"
1 Main breaker 200 Amp
1 Weatherproof breaker box 200 Amp
1 Hub for above breaker box 2 1/2"
22' Neutral Conductor #4 AWG
86' 3/0 THW Conductor (copper)for line and load side
4 Conduit straps & screws 2 1/2"
Let me know what you charge and what you think about these prices.
Thanks
Mustang
[This message has been edited by mustangelectric (edited 09-19-2004).]
#42356 09/19/04 05:00 PM
Hi Mustang.
Check out this thread in another forum about the same topic.
The prices are all over the place.
residential service
#42357 09/19/04 05:50 PM
Hi,
there is a lot of variables involved in bidding and selling electrical work..the material cost is probably pretty close all over the country..the biggest variables seem to be site conditions, labor and client.
In my area you could NOT get $4500 for a 200 Service new or upgrade!
The average price in NW Arkansas runs between $1000-$2000 for a 200A residential service.
-regards
mustang
#42358 09/19/04 06:17 PM
Southeast Pennsylvania; this is what I 'average', price varies slightly depending on the mindset of the homeowner.
100A interior panel change only: $800
100A full service: $1400
200A interior panel change only; $1400
200A full service $2400
#42359 09/19/04 06:26 PM
monolith,
that sounds fair..
thanks for the info
-regards
mustang
#42360 09/19/04 07:22 PM
CJS Offline
I get $1600 for a 100A and $2600 for a 200 Amp. That includes everything including a whole house surge protector installed out at the main.
When the panel is right on the other side of the meter I make out BIG, but when I have to run a SER cable I "earn it a little more". Either way, my prices stay the same.
#42361 09/19/04 07:41 PM
CJS Offline
One more thing:
I ALWAYS use aluminum conductors for service changes unless they specifically want copper. And I hardly ever use IMC or Rigid on a house! It's normally PVC unless I need the Rigid to support the service drop or something.
(You know, by CODE you could use #4 Cu for a 100 A residential service).
#42362 09/19/04 07:46 PM
DAYUM! For $2600 I'll throw in a surge protector AND cook 'em dinner!
$1200-$1400 here, including inspection, and I'm in NY. Not know for it's low prices.
I can't see how anyone keeps the same price for a service. Doesn't seem fair to the customer. If I have to spend another hundred on materials the customer pays for it. If the job is cake the customer pays less.
Speedy Petey
"Anyone who has never made a mistake has never tried anything new." -Albert Einstein
#42363 09/19/04 07:49 PM
Same thing here. Al URD and PVC, or SEU for risers. Typically PVC.
Speedy Petey
#42364 09/19/04 08:16 PM
what are all the steps involved in changing a 100 amp service to a 200 amp?