safety procedures #4103 09/09/01 09:16 PM
Joined: May 2001
Posts: 30
N
Nevin Offline OP
Member
what are the normal steps you take to make sure a 480volt circuit is de-energized before working on it?
1st.Open the disconnect, breaker, etc. and lock it out.
2nd.test the circuit at the point you're working at with a reliable tester.
3rd. Still making sure your hand or other part of body does not come in contact with bare conducter, disconnect it and lightly scrape it across a grounded area with your face turned away.
4. If above steps pass, work on the circuit.

How do you do it? (Always looking for better and safer procedures)

Work Gear for Electricians and the Trades
Re: safety procedures #4104 09/10/01 06:59 AM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline
Member
It is a good idea to test the ckt. beforehand as well, to ensure that it is energized prior to turning it off. Then test to make sure it is off.This way you are more sure you have the right one. We also attempt to re-start any control circuits prior to testing with a tester that is verified on a known live ckt. Also, look for indications that another circuit is within the same enclosure, and either de-energize that also, or remember to stay clear. (This got me once.)

Re: safety procedures #4105 09/10/01 08:28 AM
Joined: Aug 2001
Posts: 457
J
Jim M Offline
Member
I normally don't work on 480, but I would never verify that the power was off on any voltage by intentionally grounding it. If it were the potential for flash/thermal burns is too great.

You also may want to read the OSHA safety standard about proper protective equipment to be used around live circuits. It also covers training.

Re: safety procedures #4106 09/10/01 04:57 PM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
I agree step 3 would follow step 2 because one should never fully trust a tester.

Re: safety procedures #4107 09/10/01 05:27 PM
Joined: Aug 2001
Posts: 7,520
P
pauluk Offline
Member
Quote
Originally posted by sparky:
I agree step 3 would follow step 2 because one should never fully trust a tester.

Some of our guides suggest:

1. Verify meter on energized cct.
2. Open breaker, verify cct. dead.
3. Re-verify meter on a known live cct.

I always do 1 & 2, but I must confess to not going to step 3 on 240/415V.

Re: safety procedures #4108 09/10/01 06:07 PM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
much industry, even a local hospital in my area is poorly marked, tracers work badly due to long lengths running together. So for much of my apprenticeship i worked 277 ( 480 3 ph legs) live and thought it was the norm.

i'd be just as interested in live techniques here
[Linked Image]

Re: safety procedures #4109 09/10/01 08:21 PM
Joined: Nov 2000
Posts: 2,236
sparky66wv Offline
Member
Wow... 277 to ground live! I'm impressed...

I've never worked anything over 240V live...
I guess linemen do it every day, I just don't have the training. I've worked practically unfused service drops live, but never 277/480V...

That'll blow you several feet away if you goof, won't it? Or cook your insides...

I'm too much of a klutz to work anything over 150V to ground without some real training...

What PPE's were you using (if any)?


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: safety procedures #4110 09/10/01 08:44 PM
Joined: May 2001
Posts: 30
N
Nevin Offline OP
Member
I used to work 277v live. no more unless I have no other choice. Years ago I once was working On a 277v lighting circuit which I thought was de-energized. I had a ballast cradled in my arms while disconnecting or reconnecting it. I still don't know what touched what but what i do know is that baby became very uncomfortable in my arms. Talk about vibrating all over! I left it drop, baby, cradle, and all. That was probably the best thing that could have happened to me since at that time I had no business messing with electric, much less 277v as I now realize when I look back. I still shudder when I think of the stuff I pulled off back then. Now many years later I have become much more educated and experianced. But I am still learning. There is always room for improvement.

Re: safety procedures #4111 09/10/01 09:12 PM
Joined: Dec 2000
Posts: 4,283
electure Offline
Member
If there are 2 guys, we generally:
1. Test both of our testers.
2. Each test circuit with our own testers.
3. Each test it with the other guy's tester.
4. Disconnect & cap off the conductors while working.
5. Repeat 1-3 before reconnecting.
(I carry 2 testers in my box, and when alone generally use both).

Although I've changed out lots of fluorescent ballasts hot @ 277 (the only good use for a Wago), that's it! The company I now work for won't allow it. They lost a man about 4 yrs ago working hot 277V.
I wouldn't think of changing a wall switch or a 480 recp hot (You should see what a hot switch to ground will do to a drywall taper's knife!) [Linked Image]


[This message has been edited by electure (edited 09-10-2001).]

Re: safety procedures #4112 09/10/01 10:44 PM
Joined: Mar 2001
Posts: 85
C
CanadianSparky Offline
Member
Just a quick question here. Is your next most common voltage 277/480 after 120/208? We use 347/600 mostly. But I guess thats why there so many meters that only go to 500v,sorry, alot of things just made sense to me now.

Page 1 of 4 1 2 3 4

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
richard
richard
L.I. New York
Posts: 99
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,017 Are you busy
205,012 Re: Forum
193,127 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3