Dave, this is and is not the case.(that made alot of sense didn't it?
)
Actually in many cases the conductor is sized for the load and then the OCPD is sized to this.
Now, with out doing any math at the moment, (so don't hold me to the actual numbers)
let's look at article 430 for example.
With the applicable parts of this article we could possibly have a # 12 connected to a 45 amp breaker.
The conductor is sized for the load, the OCPD is sized to carry and start the load, and is for short circuit protection.
The OL's are actually the conductor and equipment protection here.
Of course this is not the situation or discussion in this thread.
Roger