Posted By: Randy 14-2 on 20 amp circuit - 04/04/04 02:26 PM
I posted this subject on the code forum, but would like to get other inputs on it.I've heard different views on using 14-2 soley as a swith leg on a 20 amp circuit. Is this code acceptable or not?
Posted By: Randy Re: 14-2 on 20 amp circuit - 04/04/04 02:28 PM
sorry, should be "switch" leg...
Posted By: Ryan_J Re: 14-2 on 20 amp circuit - 04/04/04 02:48 PM
No.
Posted By: Roger Re: 14-2 on 20 amp circuit - 04/04/04 04:52 PM
Randy, we can't change the answers that were given in the Code Forum, they are correct.

Why would you want to do this anyways?

BTW; If you want to edit your post for spelling (I do this more than I want to admit [Linked Image]) just click on this [Linked Image] in the top of your post.

Roger
Posted By: Randy Re: 14-2 on 20 amp circuit - 04/04/04 05:16 PM
the reason I would want to do this is the fact that 14-2 is more than capable of handling the load requirement for a single switch leg. to me 12-2 to flip a light on is over kill. Light fixtures have 18 gage on 20 amp circuits and they are handling the very same load.
Posted By: SteveMc Re: 14-2 on 20 amp circuit - 04/04/04 05:32 PM
The amperage on the 18 ga. fixture wire is limited by the wattage of the lamp. The switch wire on the other hand willl be loaded with the amperage of all the fixtures connected to it. Therefore, if you have twenty (120v) fixtures with a 100w lamp in each your circuit will be loaded to 16.7 amps and that will be the load on the 14/2 switch leg.

[This message has been edited by SteveMc (edited 04-04-2004).]
Posted By: CTwireman Re: 14-2 on 20 amp circuit - 04/04/04 08:20 PM
[Linked Image]
Posted By: iwire Re: 14-2 on 20 amp circuit - 04/04/04 08:39 PM
Instead of considering the load on this switch leg I suggest that we keep it simple.

It is a code violation.
Posted By: ga.sparky56 Re: 14-2 on 20 amp circuit - 04/04/04 10:07 PM
If there's a fire,and the insurance investigator finds that 14-2 sw.leg,whether or not that was the cause of the fire,that would be all the excuse they'ed need not to pay.

Russell
Posted By: Sir Arcsalot Re: 14-2 on 20 amp circuit - 04/05/04 11:38 PM
If someone wanted to later add a switched outlet(s) to this same circuit using the existing 14-2 there would certainly be a greater potential for the "in-wall filament" syndrome.

Just my two cents' worth.
Posted By: u2slow Re: 14-2 on 20 amp circuit - 04/06/04 04:23 AM
It is acceptable if you live in Canada [Linked Image]

30-412 allows #14 copper conductors on a 20A lighting circuit providing the luminaires they are supplying don't exceed its ampacity, and isn't over 7.5m in length.

The "ha-ha" is that we can't use a 20A lighting circuit in a dwelling unit. [Linked Image]
Posted By: SvenNYC Re: 14-2 on 20 amp circuit - 04/06/04 04:36 AM
Randy said:
Quote
to me 12-2 to flip a light on is overkill

I don't get it. I assume you already have the roll of 12 AWG wire...so what difference does a few extra feet of 12-2 down to the switch make? [Linked Image]

Isn't it just easier to follow "the good book" and be done with it?
Posted By: earlydean Re: 14-2 on 20 amp circuit - 04/06/04 04:59 PM
If you cannot even pigtail #14 Cu. to a 15 amp receptacle outlet on a 20 amp circuit, you certainly cannot use #14 Cu to run to a switch.

Fixture wire won't be used to power up anything else but that fixture. Your switch may be called upon to power up something extra, one day.
Posted By: winnie Re: 14-2 on 20 amp circuit - 04/06/04 05:02 PM
Re-reading the rules for 'tap conductors' as permitted by 240.4(E) made me gasp a couple of times. This is probably the most convoluted and non self consistent section of the code...and I think that one _could_ argue for 14ga wire on the switch loops for lamps with circuits protected at 20A.

240.4(4) references 210.19(A)(3), which says in exception 1 that a tap conductor in a 50A range circuit can be rated 20A if that is sufficient for the load served...which I take to mean that I could have a 14ga wire protected by a _50A_ breaker as long as the appliance served required less than 20A in this case. Note: looking at 210.19(A)(4) and table 210.24 seems to suggest that the authors of this article consider that a 20A rated tap conductor requires 12ga...which is not consistent with article 310... but even this interpretation clearly allows 12ga conductors protected with a 50A breaker.

240.4(4) also references 210.19(A)(4) which is just Byzantine. 210.19(A)(4) references 210.2, which basically identifies the various special purpose branch circuit articles. 210.19(A)(4) says that branch circuits other than the special purpose branch circuits or the cooking appliance branch circuits can be used with tap conductors. " Branch-circuit conductors that supply loads <other than special purpose or cooking appliances> shall have an ampacity sufficient for the loads served and shall not be smaller that 14AWG. IMHO this is explicit permission for running 14ga conductors to lamps on 20A circuits.

What follows is an Exception with a list of specific conditions for taps. This is pretty convoluted, because in general, you have a rule that creates a restriction, and then you have an exception that lifts the restriction in specific cases. But with this rule there seems to be a very broad allowance (you can use tap conductors wherever they will supply the load), followed by an exception that restricts the allowance to specific cases. Based upon the exception, 14ga taps on 20A circuits would be limited to 18" lengths, with the additional allowance in 410.67 for conductors used to connect lights requiring higher temperature wires...these taps could be up to 6 feet in length.

Needless to say, I am rather confused about how to apply the tap rules, but I rather think that the authors of the article were similarly confused about how to write the tap rules [Linked Image]

-Jon

P.S. to earlydean: the tap rules clearly differentiate between known loads and unknown receptacle loads. If a switch for a single lamp is being connected to a much larger circuit, that should be done by someone with sufficient skill to recognize the current circuit configuration and be aware of the limitations...but anyone can plug something in.
Posted By: Lostazhell Re: 14-2 on 20 amp circuit - 05/03/04 07:47 AM
It's kinda out there... but 551.43(B) says you can use 14AWG taps to 6' for recessed lights on rec vehicles [Linked Image]

-Randy
Posted By: wa2ise Re: 14-2 on 20 amp circuit - 05/04/04 01:13 AM
Well, what if a dead short should happen on the far end of the switch leg, or at the light fixture itself? You will need wire heavy enough that won't get fried by the fault current passed by the 20 amp breaker.

Another example of this is the outlet over the sink (near the ceiling) in the kitchen for the electric clock. Such clocks draw only a few watts, and thus around 30ma. Does that mean that you can run 24 gauge wire to that outlet? No, because if a short circuit ever happened at the clock, that thin wire would burn up and the breaker would think it's only someone making toast. The house might be toast....
Posted By: Randy Re: 14-2 on 20 amp circuit - 05/05/04 01:07 AM
what is the amp rating of 14 gage wire Wa2ise?
Posted By: Roger Re: 14-2 on 20 amp circuit - 05/05/04 01:39 AM
Randy, the ampacity of a conductor is not really relevant, we would have to look at resistance of the conductor and then the impedance of the combined contributors.


Roger

[This message has been edited by Roger (edited 05-04-2004).]
Posted By: wa2ise Re: 14-2 on 20 amp circuit - 05/05/04 03:09 AM
Quote
what is the amp rating of 14 gage wire

If I recall correctly, 15 amps. Much higher and the insulation will start to melt or burn. Or have I missed something?
Posted By: winnie Re: 14-2 on 20 amp circuit - 05/05/04 10:46 AM
Wa2ise,

I'd suggest taking a look at table 310.16 and 310.17. If the question is 'what is the current which can be safely carried without overheating the wire', then this NEC section allows 24A for 14ga THHN wire (with appropriate terminations, etc. etc.), and 35A for 'single conductors in free air'... even the worst case for 14ga wire, 60C insulation in a raceway allows 20A.

There is also a note referencing 240.4(D). This restricts the overcurrent protection used on 'small conductors' to 15A for 14ga wire, 20A for 12ga wire and 30A for 10ga wire. If I recall correctly, this is not to protect the wire from overload during normal operation, but instead to protect the wire during overload and short circuit conditions.

The 'unused ampacity' is available if you are in situations which require derating, say because of a large number of current carrying conductors in a single conduit, or high ambient temperatures.

-Jon
Posted By: djpep55 Re: 14-2 on 20 amp circuit - 05/05/04 12:02 PM
The wire size corresponds with the breaker size, not the load.

Dave
Posted By: Roger Re: 14-2 on 20 amp circuit - 05/05/04 07:56 PM
Dave, this is and is not the case.(that made alot of sense didn't it? [Linked Image])

Actually in many cases the conductor is sized for the load and then the OCPD is sized to this.

Now, with out doing any math at the moment, (so don't hold me to the actual numbers)
let's look at article 430 for example.

With the applicable parts of this article we could possibly have a # 12 connected to a 45 amp breaker.

The conductor is sized for the load, the OCPD is sized to carry and start the load, and is for short circuit protection.

The OL's are actually the conductor and equipment protection here.

Of course this is not the situation or discussion in this thread. [Linked Image]

Roger



[This message has been edited by Roger (edited 05-05-2004).]
Posted By: djpep55 Re: 14-2 on 20 amp circuit - 05/05/04 09:56 PM
You're so right, Roger. I'll have to do a little studying on the impedence of the combined contributors of a MOTOR switch leg. Can you help me find the table for the voltage required to beat a dead horse?

I was actually thinking of a job I bid on recently that illustrates the problem with using smaller wire for the switched pair, other than the obvious violation. In a very nice neighborhood, the homeowner had built a 3-season room. The exterior light (now in the 3-season room) had an outlet as part of the fixture. Someone other than an electrician wired the room entirely with NM, which then came out of the ceiling and was connected to a plug...into this light fixture. It included six outlets, a ceiling fan, and three exterior lights. There was another NM cord plugged into a non-GFCI exterior outlet for a TV outlet. Of course there was no WWIU cover.

Dave
Posted By: Radar Re: 14-2 on 20 amp circuit - 05/06/04 07:05 PM
I figure this string might be good for yet another posting or two.

At the simplest level, the primary function of the branch circuit breaker is to protect the downstream wiring. In order to do so, the wire must have equal or greater capacity compared to the circuit breaker.

So, the questions are:
1) Will the #14 wire be adequate for the purpose Randy has intended? Absolutely, but . . .
2) Will the #14 wire be adequately protected by a 20 amp CB, according to the NEC? Absolutely not.

It's all about protecting the wiring, not matching the wire as closely as possible to a small load. That's why we can't wire lighting circuits with 18 gage wire.

Thanks,
Radar
Posted By: wa2ise Re: 14-2 on 20 amp circuit - 05/07/04 01:48 AM
Quote
2) Will the #14 wire be adequately protected by a 20 amp CB, according to the NEC? Absolutely not.

It's all about protecting the wiring, not matching the wire as closely as possible to a small load. That's why we can't wire lighting circuits with 18 gauge wire.

That's what I thought the code wants. That if one problem happens (overcurrent due to a fault) you don't cascade to a bigger problem (house fire). Because the breaker kicks out.