Joined: Dec 2001
Posts: 270
E
Elzappr Offline OP
Member
Anyone know of a publication that gives recommendations for timing/scheduling PM's for service switchgear and mcc's? Is a 3 year cycle too frequent?

Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
NFPA 70B Recommended Practice for Electrical Equipment Maintenance 2002 Edition
Table I1 suggests even more often than that.


Ron
Joined: Apr 2002
Posts: 2,527
B
Moderator
Elz—

NETA has a (free!) download of their recommended maintenance intervals www.netaworld.org/files/ItemFileA42.pdf

Also (free!) www.usbr.gov/power/data/fist/fist4_1b/fist4_1b.pdf

And (free! pdf) nema.org/index_nema.cfm/1427/249D1875-9DE0-4504-9581AB15872B1988

Joined: Dec 2001
Posts: 270
E
Elzappr Offline OP
Member
Yeah! I suspected that there was an NFPA publication dealing with PM stuff. Thanks Ron.
I'll look into the Neta site, Bjarney. I confess that I'm not familiar with "neta".

Do we need to consult with manufacturers of all our equipment to get the real scoop for good timely predictive/preventive maintenance?

Joined: Apr 2002
Posts: 2,527
B
Moderator
Elz—

NETA members' prime business is electrical-equipment testing of new gear (acceptance testing) and existing stuff (maintenance testing).

Joined: Dec 2001
Posts: 270
E
Elzappr Offline OP
Member
This afternoon I finally got a chance to see and quickly review the NETA site, and other links. What I'm dealing with is justifying a pm schedule for the electrical service and distribution panelboards and associated transformers and wiring for office buildings that are at least 10 years old. I see a 3 to 6 year pm frequency listed throughout the 70B table for low voltage equipment, along with some scattered comments to "follow manufacturer's maintenance instructions". Are such maintenance instructions readily available, and are they practical? Or is this something that only electrical test companies are privy to? How do I find info that tells me that a certain brand and model of drawout breaker is likely to fail after x years? I suspect that this is more of an 'insider's specialty', and that the manufacturers aren't about to share that sort of failure info if they don't have to.
I realize that I'm fishing for concrete answers where there might not be any, but I appreciate any input offered. Thanks

Joined: Apr 2002
Posts: 2,527
B
Moderator
There are no easy answers. If literature is not available from the manufacturer, particularly for older gear, then experience is more important. If a facility owner has not lost money from unmaintained gear, then it can be a though sell.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Top Posters(30 Days)
Trumpy 10
Admin 10
Popular Topics(Views)
280,435 Are you busy
213,508 Re: Forum
200,398 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5