1 members (Scott35),
183
guests, and
10
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Dec 2003
Posts: 59
OP
Member
|
hi nice forum you got here. Just wondering how many here use a torque wrench on lugs? the reason i ask is because i started a new job and i was cutting in the main switchgear and the foreman of this job asked why i use a torque wrench for.I replied don't you? He said no. I was also asked why i use antishorts and twisted my wires. go figure
|
|
|
|
Joined: Feb 2004
Posts: 33
Member
|
I do use a torque wrench on large switch gear and gangable meter sockets, I thought that is why the terminals have torque specifications.
|
|
|
|
Joined: Jul 2002
Posts: 8,443 Likes: 3
Member
|
Gidday there guys, Welcome to the Board!. I've always used a Torque Wrench, and especially where the manufacturer states that one should be used. Not doing so can do nasty things, like void the warranty on the equipment!.
|
|
|
|
Joined: Feb 2004
Posts: 5
Junior Member
|
I always use a torque wrench when I have a torque spec.
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
I want to second Trumpy's welcome!
I have 3 different torque wrenches, and use all of them, afterwards making a slash mark with a sharpy (felt pen) so I make sure not to miss any. You'll find torque specs on nearly all terminations, from big switchgear down to the little branch breakers. To not torque these termination is, I believe, a violation of NEC 110.3(B) "Installation and Use Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling" Torque specs are also available from the manufacturers of mechanical lugs (Ilsco, Burndy, etc)...S
|
|
|
|
Joined: Oct 2000
Posts: 2,723 Likes: 1
Broom Pusher and Member
|
Use Torque Wrench often. Use it for setting Lugs to torque specs. Also pretwist my splices before applying the wirenut, and have never considered landing MC cable without an Anti-Short bushing (AKA Red Devil). This must make me a wierd-o?!?!?! Scott35
Scott " 35 " Thompson Just Say NO To Green Eggs And Ham!
|
|
|
|
Joined: Dec 2003
Posts: 59
OP
Member
|
That makes two of us scott! maybe he is afraid that i will make him look bad i guess. On my jobs i do things by the N.E.C and twisting wires and using anti-shorts are just commen sence.
|
|
|
|
Joined: Feb 2004
Posts: 17
Member
|
ihave a related question on this thread.
When torqing down on a lug. (whether a disco lug, ground lug or any old lug). I've seen charts which show torque setting based on the size allen and other charts based on the wire size terminating to the lug. Which do you use?
For example 3/8 allen = 32 ft lbs or 500kcmil = 24 ft lbs
|
|
|
|
Joined: Dec 2003
Posts: 59
OP
Member
|
i have never seen both for the same lug. but i have seen it this way,one for the main lugs and a seperate for the grounded and gounding lugs like you said
|
|
|
Posts: 7,383