Load Center Location #34007 01/30/04 11:41 PM
Joined: Jan 2004
Posts: 7
B
BarBeQue Offline OP
Junior Member
Howdy folks. I have a friend that wants me to upgrade his 60 amp service to a norman 200 amp. His current box is located on the side of his house. I said this is a problem, so he asks me if I can put it in his screened in back porch. ummmmm???? I told him i'd have to find out.

Work Gear for Electricians and the Trades
Re: Load Center Location #34008 01/31/04 08:49 AM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
it's cheaper to install a panel close to the original location , simply in terms of junction boxes.

but if you need to turn the location inside out (assuming it's in a noncompliant 110.26 place now) go with a nema 3R setup...

~S~

Re: Load Center Location #34009 01/31/04 06:42 PM
Joined: Jan 2004
Posts: 7
B
BarBeQue Offline OP
Junior Member
What is a Nema 3R setup? Directly on the other side of the wall is his living room and he doesnt want it placed in there. Other than on his screened in back porch, he would like to have it on in his closet. But the back porch would be an easier move. Is it legal?

Re: Load Center Location #34010 01/31/04 08:36 PM
Joined: Dec 2003
Posts: 751
E
earlydean Offline
Member
NEMA 3R is raintight
It would be OK in the screened porch, so long as nothing would be stored in front of the panel. In the closet is usually not OK, unless the closet is dedicated electrical, or huge. There must be a 36" deep x 30" wide area in front of the panel, kept clear at all times for access. 110.26
Best option, IMHO is to buy the raintight panel.
Earl


Earl
Re: Load Center Location #34011 01/31/04 09:49 PM
Joined: Dec 2000
Posts: 4,286
electure Offline
Member
If it's a clothes closet, it's never OK to put a panel in it: 240.24(D)
"Not in Vicinity of Easily Ignitible Material
Overcurrent device shall not be located in the vicinity of easily ignitible material, such as in clothes closets"
(Why is it a problem on the side of the house?)...S


[This message has been edited by electure (edited 01-31-2004).]

Re: Load Center Location #34012 02/01/04 02:42 AM
Joined: Nov 2002
Posts: 244
W
wewire2 Offline
Member
If it is a meter panel, the location has to be approved by the serving utility.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 20
Popular Topics(Views)
272,184 Are you busy
206,070 Re: Forum
194,081 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3