#34007 01/31/04 12:41 AM
Joined: Jan 2004
Posts: 7
B
Junior Member
Howdy folks. I have a friend that wants me to upgrade his 60 amp service to a norman 200 amp. His current box is located on the side of his house. I said this is a problem, so he asks me if I can put it in his screened in back porch. ummmmm???? I told him i'd have to find out.

Horizontal Ad
#34008 01/31/04 09:49 AM
Joined: Oct 2000
Posts: 5,393
S
Member
it's cheaper to install a panel close to the original location , simply in terms of junction boxes.

but if you need to turn the location inside out (assuming it's in a noncompliant 110.26 place now) go with a nema 3R setup...

~S~

#34009 01/31/04 07:42 PM
Joined: Jan 2004
Posts: 7
B
Junior Member
What is a Nema 3R setup? Directly on the other side of the wall is his living room and he doesnt want it placed in there. Other than on his screened in back porch, he would like to have it on in his closet. But the back porch would be an easier move. Is it legal?

#34010 01/31/04 09:36 PM
Joined: Dec 2003
Posts: 751
E
Member
NEMA 3R is raintight
It would be OK in the screened porch, so long as nothing would be stored in front of the panel. In the closet is usually not OK, unless the closet is dedicated electrical, or huge. There must be a 36" deep x 30" wide area in front of the panel, kept clear at all times for access. 110.26
Best option, IMHO is to buy the raintight panel.
Earl


Earl
#34011 01/31/04 10:49 PM
Joined: Dec 2000
Posts: 4,293
Member
If it's a clothes closet, it's never OK to put a panel in it: 240.24(D)
"Not in Vicinity of Easily Ignitible Material
Overcurrent device shall not be located in the vicinity of easily ignitible material, such as in clothes closets"
(Why is it a problem on the side of the house?)...S


[This message has been edited by electure (edited 01-31-2004).]

#34012 02/01/04 03:42 AM
Joined: Nov 2002
Posts: 244
W
Member
If it is a meter panel, the location has to be approved by the serving utility.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Top Posters(30 Days)
BigB 2
Popular Topics(Views)
352,649 Are you busy
276,370 Re: Forum
255,781 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5