#33473 01/21/04 11:18 AM
Joined: Feb 2002
Posts: 840
C
Member
Here is the situation. Subpanel needs to be added. Feeder to sub will be in flexible metal conduit. Main panel completely full. So 2 branch ciruits will be landed in sub panel from main panel to make room for 2 pole breaker for sub feed.

Do the neutrals for these 2 branch circuits need to be run out of the main panel to the neutral bar in the subpanel? I am thinking no because the magnetic field from the branch circuits will be cancelled by the by the sub feeders.

I have seen an entire subpanel added with 12 ciruits and not one neutral was landed on the neutral bar (all were landed in the main panel).

Peter


Peter
Horizontal Ad
#33474 01/21/04 12:41 PM
Joined: Mar 2001
Posts: 2,056
R
Member
300.20(A) would prohibit the practice you describe.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
The Watt Doctor
The Watt Doctor
Humble, TX
Posts: 440
Joined: December 2001
Top Posters(30 Days)
BigB 4
Popular Topics(Views)
327,830 Are you busy
252,684 Re: Forum
235,311 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5