Subpanel feed #33473 01/21/04 10:18 AM
Joined: Feb 2002
Posts: 840
C
CTwireman Offline OP
Member
Here is the situation. Subpanel needs to be added. Feeder to sub will be in flexible metal conduit. Main panel completely full. So 2 branch ciruits will be landed in sub panel from main panel to make room for 2 pole breaker for sub feed.

Do the neutrals for these 2 branch circuits need to be run out of the main panel to the neutral bar in the subpanel? I am thinking no because the magnetic field from the branch circuits will be cancelled by the by the sub feeders.

I have seen an entire subpanel added with 12 ciruits and not one neutral was landed on the neutral bar (all were landed in the main panel).

Peter


Peter
Work Gear for Electricians and the Trades
Re: Subpanel feed #33474 01/21/04 11:41 AM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline
Member
300.20(A) would prohibit the practice you describe.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 7,218
Joined: April 2002
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 17
Popular Topics(Views)
272,155 Are you busy
206,034 Re: Forum
194,056 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3