1 members (Scott35), 565 guests, and 35 robots.
#28806 08/31/03 02:33 PM
Eandrew Offline OP
I wanted to clarify my understanding of single phase on a three phase system:
single phase:
120v = one pole breaker
240v = two pole breaker
three phase:
120v or 277v single phase = one pole breaker
208v or 480v single phase = 2 pole breaker
208v or 480v three phase = 3 pole breaker
208v or 480v
#28807 08/31/03 02:46 PM
You can have a single-phase circuit tapped from a three-phase supply either by connected phase-to-phase, or phase-to-neutral.
The breaker needs to open all ungrounded conductors, so with a 3-ph wye system a phase-to-phase load needs a 2-pole C/B, while a phase-to-neutral load needs only a single-pole, as you've stated.
The only cases that might want adding to your list would be something like a corner-grounded 240V delta, where one of the phases is actually grounded.
#28808 08/31/03 02:54 PM
Eandrew Offline OP
thanks paul. this forum is always a good place to turn to when your not sure. Thanks again.
