Service #2805
07/25/01 10:05 PM
07/25/01 10:05 PM
E
evan  Offline OP
Junior Member
Joined: Jul 2001
Posts: 1
Fancy Farm KY
I noticed in the code that a service head had do be atleast three feet from a window.

How far does a meter base have to be from a window.


evan elder
Work Gear for Electricians and the Trades
Re: Service #2806
07/26/01 07:18 AM
07/26/01 07:18 AM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,901
NY, USA
Evan,

Welcome!
Our local utility (LI, NY) requires that it not be under a window. Other than that I don't know of any other rules on the subject. Maybe you have a local requirement.

Bill

Re: Service #2807
07/27/01 08:12 AM
07/27/01 08:12 AM
C
cinkerf  Offline
Member
Joined: Dec 2000
Posts: 84
Pittsburgh, Pennsysvania. ...
Evan,

Our local power company provides a small code book of their own. I couldn't find a rule concerning placement near window. In the past I've installed meter enclosures less than three feet from window and had no problem with it passing elec. inspection. Mounting height must be five to six feet.

Frank

Re: Service #2808
07/27/01 08:42 AM
07/27/01 08:42 AM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,901
NY, USA
Evan,

Just as a comparison to Frank's comments, We are allowed a height of 3 to 6 ft. So, you see everywhere can be different. It's not a code requirement.

Bill

Re: Service #2809
07/27/01 11:39 AM
07/27/01 11:39 AM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
My take on it..

I believe this clearance issue is rooted in 230-9, which requires claerance for open conductors without an overall jacket. The service drop, which is spliced at the service head is typically open conductors, and therefore subject to the clearance requirements. The service entrance conductors, which may be jacketed SE Cable would not be subject ot the clearances due to the overall jacket, and may pass closer to windows etc.
This probably would apply to the meter socket as well, unless local or utility rules prohibit it.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 11
sparky 10
Popular Topics(Views)
249,284 Are you busy
187,219 Re: Forum
176,579 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.9668 MB (Peak: 1.1064 MB) Zlib enabled. Server Time: 2018-09-19 14:55:49 UTC