Service #2805 07/25/01 10:05 PM
Joined: Jul 2001
Posts: 1
E
evan Offline OP
Junior Member
I noticed in the code that a service head had do be atleast three feet from a window.

How far does a meter base have to be from a window.


evan elder
Work Gear for Electricians and the Trades
Re: Service #2806 07/26/01 07:18 AM
Joined: Oct 2000
Posts: 3,961
Bill Addiss Offline
Member
Evan,

Welcome!
Our local utility (LI, NY) requires that it not be under a window. Other than that I don't know of any other rules on the subject. Maybe you have a local requirement.

Bill


Bill
Re: Service #2807 07/27/01 08:12 AM
Joined: Dec 2000
Posts: 84
C
cinkerf Offline
Member
Evan,

Our local power company provides a small code book of their own. I couldn't find a rule concerning placement near window. In the past I've installed meter enclosures less than three feet from window and had no problem with it passing elec. inspection. Mounting height must be five to six feet.

Frank

Re: Service #2808 07/27/01 08:42 AM
Joined: Oct 2000
Posts: 3,961
Bill Addiss Offline
Member
Evan,

Just as a comparison to Frank's comments, We are allowed a height of 3 to 6 ft. So, you see everywhere can be different. It's not a code requirement.

Bill


Bill
Re: Service #2809 07/27/01 11:39 AM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline
Member
My take on it..

I believe this clearance issue is rooted in 230-9, which requires claerance for open conductors without an overall jacket. The service drop, which is spliced at the service head is typically open conductors, and therefore subject to the clearance requirements. The service entrance conductors, which may be jacketed SE Cable would not be subject ot the clearances due to the overall jacket, and may pass closer to windows etc.
This probably would apply to the meter socket as well, unless local or utility rules prohibit it.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,961
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,031 Are you busy
205,036 Re: Forum
193,149 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3