1 members (Scott35), 175 guests, and 11 robots.
#27886 08/08/03 12:07 AM
Carnak Offline OP
Update
The 416V transformers feed GE panel boards rated for 480/277. The single pole breakers are rated for 277V.
My concern here was I have never seen an air conditioning unit fed with a 240 hot and a neutral. The PTACs are all by GE so I have a call in to them.
A majority of the PTACs have been in service since 1989,so I am really wondering if I have been worried about nothing.
Go Big or Stay Home
#27887 08/08/03 05:51 AM
Wouldn't most American 240V A/C units (at least those intended for commercial use) be listed for more than 150V to ground?
They would need to be so rated for operation on a 240V corner-grounded delta supply, or if one side were connected to the high leg (208V) of a 4-wire delta.
#27888 08/08/03 06:32 AM
BTW,
What does PTAC mean?
#27889 08/09/03 07:05 PM
Carnak Offline OP
PTAC- something to the effect of "Packaged Terminal Air Conditioner", the through-the-wall units you see in a lot of motels.
I think my concern boils down to does a motor 'care' how it is getting its power as long as the voltage, phase and frequency are correct.
It looks like the answer is no, the motor does not care.
I asked the manufacturer's engineer, and he spent a couple hours going through the NEC and could find nothing wrong.
The 150 to ground issue is not a problem with 3 phase equipment in a building powered by 240 open delta.
Go Big or Stay Home