#27757 07/31/03 09:00 PM
Joined: Feb 2002
Posts: 840
C
Member
I know this is a "dead horse" topic, but I'm still confused about it. This subject seems to be a source of mass confusion in the electrical trade.

So, as an example, here is an a/c unit nameplate (from an 2 ton Trane unit):

Min circuit ampacity: 15 amps

Min fuse/breaker size: 20 amps

Max fuse/breaker size: 25 amps

Line running amps: 11 amps


Does this mean that the unit can be fed by #14 protected by a 20 amp breaker?

Or #12 on a 20 amp breaker?


Do you size the conductors by the "minimum ampacity," and size the breaker by "minimum fuse/breaker"? [Linked Image]

One thing I do understand is that in this situation, the breaker only provides short-circuit protection, as the motor is protected by a thermal overload device.
-Peter


Peter
Horizontal Ad
#27758 07/31/03 10:37 PM
Joined: Nov 2000
Posts: 2,148
R
Member
In this case the code would permit #14 on a 25 amp breaker.
Don


Don(resqcapt19)
#27759 08/01/03 12:53 AM
Joined: Aug 2002
Posts: 141
E
Member
A/C unit: 120/208 V 3 phase
Nameplate reads:
18.2 amps FLA.
Min. circuit: 31.5 amps
I had to replace the 30 amp disconnect and #10 wire with a 50 amp disconnect (40 amp disconnect not available) and run #8 wire.

#27760 08/01/03 06:52 AM
Joined: Mar 2001
Posts: 2,056
R
Member
Bob,
Were you using NM Cable?
If not, it seems you were in compliance with 310.16, which lists #10 as rated for 35 amps.
As far as having to upsize the disconnect, I think you need to know the Locked Rotor Current so you can back-calculate using Table 430.151(B).

#27761 08/01/03 10:25 AM
Joined: Aug 2002
Posts: 141
E
Member
Thanks Redsy. I was going to pull 4#10's but the inspector said I needed #8 for the 31.5 amps. I was a little suprised to say the least. He is coming out for an inspection on some other gear next week. I will ask him again before I do the pull.

#27762 08/01/03 05:01 PM
Joined: Mar 2001
Posts: 2,056
R
Member
Bob,
He may be thinking about the asterisk at the bottom of Table 310.16, which refers to 240.4(D).
However, 240.4(D) refers to 240.4(G), which permits particular Articles to specify conductor ampacity selections.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Top Posters(30 Days)
BigB 2
Popular Topics(Views)
353,524 Are you busy
277,362 Re: Forum
256,299 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5