Power Loss in Terminations #24530 04/16/03 11:56 AM
Joined: Oct 2001
Posts: 597
E
ElectricAL Offline OP
Member
A client contacted me yesterday to ask if I had heard about how to save $$$ on the power bill. My client was contacted by a firm that, after relanding cable terminations, would split the power bill savings with them.

[b]This links to the basic idea.[/b]

Any one run into this?


Al Hildenbrand
Work Gear for Electricians and the Trades
Re: Power Loss in Terminations #24531 04/16/03 12:21 PM
Joined: May 2001
Posts: 552
T
txsparky Offline
Member
Things that make you go Hmmmmm......! [Linked Image]

I'm curious as to what is used on the terminations ? Is the product UL listed for use on the equipment involved ? Is the equipment UL listed for use with this product ? Is the wire involved listed for use with this product ? Lotsa Quetions



[This message has been edited by txsparky (edited 04-16-2003).]


Donnie
Re: Power Loss in Terminations #24532 04/16/03 12:40 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
Look at a 240 volt single phase circuit with an 80 amp load. To reduce the current by 16% you would have to reduce the I²R losses by more than 3000 watts at the termination. I really don't believe that a termination has 3000 watts of loss and if it does, it won't last very long before it melts down.
Don


Don(resqcapt19)
Re: Power Loss in Terminations #24533 04/16/03 01:07 PM
Joined: Jul 2002
Posts: 8,377
Trumpy Offline
Member
ElectricAL,
This scheme sounds very dodgy, if it's so good, why isn't it used more widely and why wasn't it used years ago?, or has it and it didn't give any lasting results.
Also, you can't escape the laws of Physics and nature that easily!. [Linked Image]

Re: Power Loss in Terminations #24534 04/16/03 04:44 PM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
It appears that you pay the company their share of the supposed yearly savings up front "and instead of paying your local electric provider, you keep a portion and pay EII a portion". You then get your payback from your future utility bills.

Also don't forget to factor in the cost of your plant "down time" when calculating your potential savings.

Re: Power Loss in Terminations #24535 04/16/03 05:23 PM
Joined: Apr 2002
Posts: 2,527
B
Bjarney Offline
Moderator
Suggest your client not waste time calling "them" back.

For their magic process to work, spices and terminations would have to be blistering hot, and there will likely be other complaints before that point. Think about this for a bit—it makes good sense.

You can prove it to yourself with a POWER-RATED multimeter on a low-range AC-volt scale. Voltage drop can be carefully but literally measured across cable-to-lug joints—then multiplied by the current through the joint. Roughly, millivolts x amperes = milliwatts of power dissipation in the joint.

{A reference is http://ecmweb.com/ar/electric_testing_contact_quality/index.htm Testing Contact Quality on Live Motor Starters—based on another short EC&M article by me; published in the mid 1990s. A similar discussion is http://ecmweb.com/ar/electric_troubleshooting_electrical_problems/index.htm A significant advance in a number of multimeters is that appropriately-rated meters will not be damaged by accidental application of line voltage while in a millivolt range: this makes the technique workable.}

Re: Power Loss in Terminations #24536 04/17/03 06:58 AM
Joined: Jul 2002
Posts: 175
E
electric-ed Offline
Member
If anyone is tempted to go for this, I would advise them to keep a very close watch on these guys while they do their "measurements".

Ed

Re: Power Loss in Terminations #24537 04/17/03 07:05 AM
Joined: Aug 2001
Posts: 7,520
P
pauluk Offline
Member
I'd tell the client to forget about calling them as well. It doesn't add up.

Re: Power Loss in Terminations #24538 04/17/03 08:01 AM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline
Member
And while you're watching your utility bills decline, the special electrochemical emits anti-oxidants that are rich in beta carotene. Your excess weight magically melts away with no need for exercise, your hair grows back, and your cholesterol levels drop while you sleep.

This stuff should be sold on a cable TV channel at 5:00 AM.

Re: Power Loss in Terminations #24539 04/17/03 09:57 AM
Joined: May 2001
Posts: 552
T
txsparky Offline
Member
LOL @ Redsy,.. [Linked Image] [Linked Image]......Sign me up !! I've got all of the symptoms !!!!!!


Donnie
Page 1 of 7 1 2 3 4 5 6 7

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 