Swimming Pool question #219817 11/30/18 01:47 PM
Joined: Jan 2004
Posts: 1,498
G
George Little Offline OP
Member
When I read 680.23 (A)(3) it says that the GFCI requirement for underwater luminaires should be in the branch circuit. Does this mean that a sub panel protected with a GFCI Main will not satisfy the requirements in 680.23(A)(3)? I say we still need a GFCI in the branch circuit. Note that it doesn't specify a "GFCI in the branch Circuit" when talking about the pool cover, motors or other items needing GFCI protection. Only that they must have GFCI protection.


George Little
2017 / 2014 NEC & Related Books and Study Guides
Re: Swimming Pool question [Re: George Little] #219820 11/30/18 02:17 PM
Joined: Jul 2004
Posts: 9,409
G
gfretwell Offline
Member
I suspect that is just language left over from when the GFCI requirement first arrived and a feeder style was not available. I guess to be totally compliant you would need a GFCI breaker or dead front device in the light circuit but it does sound redundant.


Greg Fretwell
Re: Swimming Pool question [Re: gfretwell] #219821 11/30/18 03:56 PM
Joined: Jan 2004
Posts: 1,498
G
George Little Offline OP
Member
Greg, I don't think it's a matter of an oversight on apart of the code panel. I think they prefer to have individual GFCI protection on the pool light. The code panel is rather anal about being accurate. There probably is substantial reason for leaving it in there as "branch circuit". Be interested in know what some of the other members think. Who knows, might even hear from someone on code panel 17.


George Little
Re: Swimming Pool question [Re: George Little] #219826 12/02/18 05:57 PM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
I agree with George.
The folks on the Code panels are very meticulous about what they write.

I get into regular arguments with Mechanical types who think that the requirement for a receptacle within 25 feet of Heating and Air Conditioning units should apply to all HVAC equipment.
The Code panel wrote it the way that they did to deliberately exclude ventilation (fans) since there is never a need for portable test or service equipment to be plugged in when working on a fan.
Heating and Air Conditioning units have controls and refrigerant lines that need to be evacuated...fan motors do not.

If they are calling for individual GFCI protection on the branch circuit that's exactly what they want there.


Ghost307
Re: Swimming Pool question [Re: George Little] #219827 12/03/18 02:21 PM
Joined: Apr 2002
Posts: 7,121
HotLine1 Offline
Member
I have to agree with George. The Pool lighting circuit protected by a GFCI on the branch circuit. I have not had anyone say that it is protected by the pool sub panel.

As to Ghosts comment regarding fans, as he said, there is no reason for a receptacle within 25'.


John
Re: Swimming Pool question [Re: George Little] #219829 12/04/18 12:59 PM
Joined: Jul 2004
Posts: 9,409
G
gfretwell Offline
Member
I understand the rule but if you trust GFCIs one in the feeder should provide the same protection. With pool lights moving to low voltage LEDs the question might be moot anyway. A GFCI on the primary to the transformer will not provide any protection on the secondary anyway.

Last edited by gfretwell; 12/04/18 01:00 PM.

Greg Fretwell
Re: Swimming Pool question [Re: gfretwell] #219831 12/04/18 01:48 PM
Joined: Jan 2004
Posts: 1,498
G
George Little Offline OP
Member
Greg– you are correct as usual, but in this case I suspect that the panel left it alone so that a problem on the circuit would only shut down the circuit. (Hopefully) This would allow the rest of the pool equipment to continue running. I'm sure the GFCI on the panel should trip at the 4-6ma level so who knows which one will trip. I'm still enforcing branch circuit GFCI when I inspect. Don't need to stand before 12 honest men/women and justify why I didn't make the right call. 🤪


George Little
Re: Swimming Pool question [Re: George Little] #219833 12/04/18 09:41 PM
Joined: Jul 2004
Posts: 9,409
G
gfretwell Offline
Member
I agree with you that as long it is there, I am enforcing any GFCI rule. That is the most important innovation to save lives in the history of electricity.
I am always arguing with people about refrigerators and sump pumps that trip GFCIs. They are broken and should be repaired or retired, not bootlegged on a non-GFCI circuit.

Put one of those old style 2 prong adapters on the plug, ground the pigtail and loop it through a current probe on a scope, fight is over. On a sump pump, your clamp works to make your point. On a fridge, A/C or whatever, you are seeing the electrical representation of a thunderstorm inside that compressor.
Then I ask, "wanna unhook that ground and hold the pigtail"?
Still no takers.


Greg Fretwell
Re: Swimming Pool question [Re: George Little] #219834 12/05/18 01:37 PM
Joined: Apr 2002
Posts: 7,121
HotLine1 Offline
Member
Yes, I don't need to stand next to, or with George, and try to explain why I went away from the NEC.

As to Greg's analogy, I add..."you want to be a conductor??" of electricity,, not the train.


John

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Show All Member Profiles 
Top Posters(30 Days)
sparky 10
Popular Topics(Views)
259,726 Are you busy
195,066 Re: Forum
184,472 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3