two 15 HP 480 pumps VFD's Located in building 800 feed away. ( Pumps in a flood plane area) . Is there a Problem running two feeders from VFD;s in same conduit the 800 Ft . The reason I ask is I heard there could be a interference problem between cables in the same raceway. They know they might lose the pumps but want to keep the VFD's out of harms way. Yoopersup
|
|
|
|
Joined: Jul 2004
Posts: 10,006 Likes: 37
Member
|
If the feeders were twisted it should eliminate the cross talk but I am not sure how you do that unless you pull a cable that is twisted (like SER) At the frequencies we are talking about you don't really need that much twist. You might be able to get a twist in each set as you are feeding them in. Are you doing this all in one pull?
Greg Fretwell
|
|
|
|
Joined: May 2005
Posts: 984 Likes: 1
Member
|
I wouldn't only be worried about crosstalk; I'd be concerned about the 800 foot distance between the VFD and the motor unless appropriate filters are installed.
Ghost307
|
|
|
|
Joined: Jul 2004
Posts: 10,006 Likes: 37
Member
|
Voltage drop will be tough too. figuring FLA at around 20a, you need #6 cu to keep the drop around 3%
Greg Fretwell
|
|
|
|
Joined: Mar 2003
Posts: 849
OP
Member
|
1 conductors per phase utilizing a #4 Copper conductor will limit the voltage drop to 2.49% or less when supplying 30.0 amps for 800 feet on a 480 volt system. For Engineering Information Only: 70.0 Amps Rated ampacity of selected conductor 0.2957 Ohms Resistance (Ohms per 1000 feet) 0.048 Ohms Reactance (Ohms per 1000 feet) 14.399999999999999 volts maximum allowable voltage drop at 3% 11.933. Actual voltage drop loss at 2.49% for the circuit 0.9 Power Factor
21 amps x 125% =26.25 round up to 30 amps for safety .
|
|
|