ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
This Old House
by johno12345. 05/26/18 12:44 PM
Extension cords
by LongRunner. 05/25/18 12:19 PM
Fire source!
by LongRunner. 05/25/18 01:49 AM
Alternative income sources
by gfretwell. 05/24/18 10:07 PM
Furnace igniter leaking noise to stereo
by geoff in UK. 05/23/18 01:18 PM
New in the Gallery:
Plug terminals
Housebilding DIY wiring
Who's Online Now
0 registered members (), 26 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
VFD MotorFeeders #218803
10/17/17 09:50 AM
10/17/17 09:50 AM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 840
Michigan
two 15 HP 480 pumps VFD's Located in building 800 feed away. ( Pumps in a flood plane area) .
Is there a Problem running two feeders from VFD;s in same conduit the 800 Ft .
The reason I ask is I heard there could be a interference problem between cables in the same
raceway. They know they might lose the pumps but want to keep the VFD's out of harms way.
Yoopersup

2017 / 2014 NEC & Related Books and Study Guides
Re: VFD MotorFeeders [Re: Yoopersup] #218804
10/17/17 10:01 PM
10/17/17 10:01 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,225
Estero,Fl,usa
If the feeders were twisted it should eliminate the cross talk but I am not sure how you do that unless you pull a cable that is twisted (like SER)
At the frequencies we are talking about you don't really need that much twist. You might be able to get a twist in each set as you are feeding them in.
Are you doing this all in one pull?


Greg Fretwell
Re: VFD MotorFeeders [Re: Yoopersup] #218805
10/18/17 02:39 PM
10/18/17 02:39 PM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 943
Chicago Illinois USA
I wouldn't only be worried about crosstalk; I'd be concerned about the 800 foot distance between the VFD and the motor unless appropriate filters are installed.


Ghost307
Re: VFD MotorFeeders [Re: Yoopersup] #218807
10/19/17 01:02 AM
10/19/17 01:02 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,225
Estero,Fl,usa
Voltage drop will be tough too. figuring FLA at around 20a, you need #6 cu to keep the drop around 3%


Greg Fretwell
Re: VFD MotorFeeders [Re: Yoopersup] #218811
10/22/17 07:52 PM
10/22/17 07:52 PM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 840
Michigan
1 conductors per phase utilizing a #4 Copper conductor will limit the voltage drop to 2.49% or less when supplying 30.0 amps for 800 feet on a 480 volt system.
For Engineering Information Only:
70.0 Amps Rated ampacity of selected conductor
0.2957 Ohms Resistance (Ohms per 1000 feet)
0.048 Ohms Reactance (Ohms per 1000 feet)
14.399999999999999 volts maximum allowable voltage drop at 3%
11.933. Actual voltage drop loss at 2.49% for the circuit
0.9 Power Factor

21 amps x 125% =26.25 round up to 30 amps for safety .


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,891
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
twh 7
Popular Topics(Views)
246,942 Are you busy
184,345 Re: Forum
173,548 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 15 (0.004s) Memory: 0.9676 MB (Peak: 1.1095 MB) Zlib enabled. Server Time: 2018-05-27 23:15:45 UTC