Doing fill calculations .
Copper & Alum same conductor size , Same insulation ,
Same OD ????
Yoopersup

Horizontal Ad
Joined: Jul 2004
Posts: 10,006
Likes: 37
G
Member
I am not aware of any table that shows them being different unless we are talking about "compact conductors" and I have never seen that in copper.


Greg Fretwell
Joined: Mar 2003
Posts: 849
Y
Member
I haven;t seen any charts that say they are different .
Only way to be sure I get is get manufacturers specs on both.
Thank you

Joined: Jul 2004
Posts: 10,006
Likes: 37
G
Member
As an inspector, I think we have done our due diligence if we just follow the tables in the back of the NEC. As in installer you have to understand if you up size the raceway or the box over the minimum, your job is easier. It will not be as hard to pull in the conductors and easier to put the box together. It is like wire bending space. I can tell someone what the minimum size is but I still do not actually have to bend that conductor to make that turn. wink


Greg Fretwell
Joined: Mar 2003
Posts: 849
Y
Member
Always depends on which side the Fence your on with a project.
As four starters we have 6000 plus feet of 6 inch HDPE full of
HV cable for starters . I want it to Code (as Always) . Having pulled a lot of wire myself
I know what you mean. As Always I thank you & others on this Forum for your imputes.
Thank you
Yoopersup

Joined: Apr 2002
Posts: 7,411
Likes: 7
Member
Just as a side FYI, the LBs, LLs, LRs, etc have fill issues. As far as I know, there should not be any differences between Cu and Al conductors with the same insulation. As Greg mentioned, exclude the 'compact' ,

When I had 'tools', the pipe was upsized to make life easier.


John
Joined: May 2005
Posts: 984
Likes: 1
G
Member
Whenever I have a long or twisty run I call out for the conduit to be increased by a trade size.
Unless I end up with someone who spends a dollar to save a penny and skinnies down the conduit it always works out being the same installed price...or a bit less.


Ghost307
Horizontal Ad

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
HappyElectrician
HappyElectrician
Penn USA
Posts: 31
Joined: December 2011
Top Posters(30 Days)
Popular Topics(Views)
347,089 Are you busy
272,200 Re: Forum
252,559 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5