Main lug panels #217419 07/26/16 01:20 PM
Joined: Oct 2002
Posts: 830
S
sparkync Offline OP
Member
Where in the code does it explain about using main lug panels. I'm going about 220ft. from a main breaker panel, feeding a 100 amp panel. Normally I would use a main breaker panel anyway, but so far I don't seem to find one that fits my need.
thanks

2017 / 2014 NEC & Related Books and Study Guides
Re: Main lug panels [Re: sparkync] #217420 07/26/16 01:59 PM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
I don't think it does.
I always like using a panel with a Main because it reduces the temptation to work it hot when someone doesn't want to walk to the feeder breaker and turn it off...but I don't think there's a requirement for a main.


Ghost307
Re: Main lug panels [Re: sparkync] #217421 07/27/16 02:48 AM
Joined: Jul 2004
Posts: 9,412
G
gfretwell Offline
Member
A main is only required if it is in another building and they do not use the 225.32 ex1 excuse "documented safe switching procedures".

When they are not within sight, I am not really happy but it is legal. Good documentation of where the feeder breaker is should be on the MLO.


Greg Fretwell
Re: Main lug panels [Re: sparkync] #217422 07/27/16 03:30 PM
Joined: Apr 2002
Posts: 7,122
HotLine1 Offline
Member
Greg:
I agree with you.

How do you feel IF the sub has only 4 single pole branches?

Think the old six switch rule!



John
Re: Main lug panels [Re: sparkync] #217425 07/27/16 05:18 PM
Joined: Jul 2004
Posts: 9,412
G
gfretwell Offline
Member
That does not really address the hot bus but I suppose there are still hot components in a panel with a main. (Unless you are in Canada where they have a cover over the main lugs from what I understand)


Greg Fretwell
Re: Main lug panels [Re: sparkync] #217428 07/28/16 09:26 PM
Joined: Apr 2002
Posts: 7,122
HotLine1 Offline
Member
Greg:

IMHO, the 'six switch rule' was OK back when there were limited circuits compared to today.

On the commercial side, the $$$ saved by eliminating the main, catches up when the buildings are renovated. Quite a few show up each year.



John
Re: Main lug panels [Re: sparkync] #217429 07/29/16 03:07 AM
Joined: Jul 2004
Posts: 9,412
G
gfretwell Offline
Member
I understand that it is not a huge hazard. I suppose I was just saying identifying where it comes from is a good idea for that time when you are working on something more complicated than a branch circuit.


Greg Fretwell

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 69
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
BigB 5
Trumpy 1
Popular Topics(Views)
260,727 Are you busy
195,761 Re: Forum
185,149 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3