Main lug panels #217419
07/26/16 02:20 PM
07/26/16 02:20 PM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
Where in the code does it explain about using main lug panels. I'm going about 220ft. from a main breaker panel, feeding a 100 amp panel. Normally I would use a main breaker panel anyway, but so far I don't seem to find one that fits my need.
thanks

2017 / 2014 NEC & Related Books and Study Guides
Re: Main lug panels [Re: sparkync] #217420
07/26/16 02:59 PM
07/26/16 02:59 PM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 945
Chicago Illinois USA
I don't think it does.
I always like using a panel with a Main because it reduces the temptation to work it hot when someone doesn't want to walk to the feeder breaker and turn it off...but I don't think there's a requirement for a main.


Ghost307
Re: Main lug panels [Re: sparkync] #217421
07/27/16 03:48 AM
07/27/16 03:48 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,242
Estero,Fl,usa
A main is only required if it is in another building and they do not use the 225.32 ex1 excuse "documented safe switching procedures".

When they are not within sight, I am not really happy but it is legal. Good documentation of where the feeder breaker is should be on the MLO.


Greg Fretwell
Re: Main lug panels [Re: sparkync] #217422
07/27/16 04:30 PM
07/27/16 04:30 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,985
Brick, NJ USA
Greg:
I agree with you.

How do you feel IF the sub has only 4 single pole branches?

Think the old six switch rule!



John
Re: Main lug panels [Re: sparkync] #217425
07/27/16 06:18 PM
07/27/16 06:18 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,242
Estero,Fl,usa
That does not really address the hot bus but I suppose there are still hot components in a panel with a main. (Unless you are in Canada where they have a cover over the main lugs from what I understand)


Greg Fretwell
Re: Main lug panels [Re: sparkync] #217428
07/28/16 10:26 PM
07/28/16 10:26 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,985
Brick, NJ USA
Greg:

IMHO, the 'six switch rule' was OK back when there were limited circuits compared to today.

On the commercial side, the $$$ saved by eliminating the main, catches up when the buildings are renovated. Quite a few show up each year.



John
Re: Main lug panels [Re: sparkync] #217429
07/29/16 04:07 AM
07/29/16 04:07 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,242
Estero,Fl,usa
I understand that it is not a huge hazard. I suppose I was just saying identifying where it comes from is a good idea for that time when you are working on something more complicated than a branch circuit.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,121 Are you busy
185,579 Re: Forum
174,897 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 15 (0.003s) Memory: 0.9858 MB (Peak: 1.1414 MB) Zlib enabled. Server Time: 2018-07-19 01:37:16 UTC