ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Burning out of return(white) side of 120volt rec
by crselectric. 06/14/19 02:15 AM
Video door bell causing chime activation of coil
by JoeTestingEngr. 06/13/19 12:43 PM
Troubleshooting Voltage Drop Across Relay
by gfretwell. 06/09/19 11:49 AM
Apple Recalls Three-Prong Wall Plug Adapters
by Admin. 06/05/19 09:06 PM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 3 guests, and 17 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Main lug panels #217419
07/26/16 02:20 PM
07/26/16 02:20 PM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
Where in the code does it explain about using main lug panels. I'm going about 220ft. from a main breaker panel, feeding a 100 amp panel. Normally I would use a main breaker panel anyway, but so far I don't seem to find one that fits my need.
thanks

2017 / 2014 NEC & Related Books and Study Guides
Re: Main lug panels [Re: sparkync] #217420
07/26/16 02:59 PM
07/26/16 02:59 PM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 978
Chicago Illinois USA
I don't think it does.
I always like using a panel with a Main because it reduces the temptation to work it hot when someone doesn't want to walk to the feeder breaker and turn it off...but I don't think there's a requirement for a main.


Ghost307
Re: Main lug panels [Re: sparkync] #217421
07/27/16 03:48 AM
07/27/16 03:48 AM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,365
Estero,Fl,usa
A main is only required if it is in another building and they do not use the 225.32 ex1 excuse "documented safe switching procedures".

When they are not within sight, I am not really happy but it is legal. Good documentation of where the feeder breaker is should be on the MLO.


Greg Fretwell
Re: Main lug panels [Re: sparkync] #217422
07/27/16 04:30 PM
07/27/16 04:30 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,091
Brick, NJ USA
Greg:
I agree with you.

How do you feel IF the sub has only 4 single pole branches?

Think the old six switch rule!



John
Re: Main lug panels [Re: sparkync] #217425
07/27/16 06:18 PM
07/27/16 06:18 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,365
Estero,Fl,usa
That does not really address the hot bus but I suppose there are still hot components in a panel with a main. (Unless you are in Canada where they have a cover over the main lugs from what I understand)


Greg Fretwell
Re: Main lug panels [Re: sparkync] #217428
07/28/16 10:26 PM
07/28/16 10:26 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,091
Brick, NJ USA
Greg:

IMHO, the 'six switch rule' was OK back when there were limited circuits compared to today.

On the commercial side, the $$$ saved by eliminating the main, catches up when the buildings are renovated. Quite a few show up each year.



John
Re: Main lug panels [Re: sparkync] #217429
07/29/16 04:07 AM
07/29/16 04:07 AM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,365
Estero,Fl,usa
I understand that it is not a huge hazard. I suppose I was just saying identifying where it comes from is a good idea for that time when you are working on something more complicated than a branch circuit.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
lil suzi
lil suzi
Midwest
Posts: 57
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
255,689 Are you busy
191,665 Re: Forum
181,445 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 15 (0.004s) Memory: 0.9860 MB (Peak: 1.1416 MB) Zlib enabled. Server Time: 2019-06-16 06:55:48 UTC