Photos of the Week:
Meter vs Bricklayer
Meter vs Bricklayer
0 members (), 32 guests, and 17 robots.
#217419 07/26/16 02:20 PM
Where in the code does it explain about using main lug panels. I'm going about 220ft. from a main breaker panel, feeding a 100 amp panel. Normally I would use a main breaker panel anyway, but so far I don't seem to find one that fits my need.
thanks
I don't think it does.
I always like using a panel with a Main because it reduces the temptation to work it hot when someone doesn't want to walk to the feeder breaker and turn it off...but I don't think there's a requirement for a main.
Ghost307
A main is only required if it is in another building and they do not use the 225.32 ex1 excuse "documented safe switching procedures".
When they are not within sight, I am not really happy but it is legal. Good documentation of where the feeder breaker is should be on the MLO.
Greg:
I agree with you.
How do you feel IF the sub has only 4 single pole branches?
Think the old six switch rule!
That does not really address the hot bus but I suppose there are still hot components in a panel with a main. (Unless you are in Canada where they have a cover over the main lugs from what I understand)
Greg:
IMHO, the 'six switch rule' was OK back when there were limited circuits compared to today.
On the commercial side, the $$$ saved by eliminating the main, catches up when the buildings are renovated. Quite a few show up each year.
I understand that it is not a huge hazard. I suppose I was just saying identifying where it comes from is a good idea for that time when you are working on something more complicated than a branch circuit.