Outdoor transformer/grounding question #217353
06/23/16 02:10 AM
06/23/16 02:10 AM
S
Sparky42  Offline OP
New Member
Joined: Jun 2016
Posts: 2
CA
Application is an outdoor 30kVA, 480V/400V step down delta-wye transformer to be located within 10 feet of a building panel breaker box. The box has three phase 480V fused power and an input ground wire tied to the breaker box via a screw lug. The output is a 3P4W IEC-309 receptacle, the ground pin of the receptacle has a wire that screws into the breaker box. My question is: Can I use the receptacle ground wire to be the ground for the transformer chassis and X0 of the secondary (via a terminal bar inside and bonded to the transformer enclosure)? Or will I have to run a ground wire independent of the receptacle so that ground is always made regardless of if the plug is in the receptacle. I could not find this detail in NEC.

2017 / 2014 NEC & Related Books and Study Guides
Re: Outdoor transformer/grounding question [Re: Sparky42] #217354
06/23/16 03:20 AM
06/23/16 03:20 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,254
Estero,Fl,usa
I suppose you need to back up and see if that transformer is listed for cord and plug connection. If that is OK, I suppose the pin in the plug is sufficient to establish the ground.
Those 309 plugs are designed so the ground makes before the ungrounded pins.


Greg Fretwell
Re: Outdoor transformer/grounding question [Re: Sparky42] #217387
07/01/16 12:59 AM
07/01/16 12:59 AM
Y
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 845
Michigan
Read 2014 N.E.C. 250.30 (C)

Re: Outdoor transformer/grounding question [Re: Sparky42] #217393
07/05/16 12:09 AM
07/05/16 12:09 AM
S
Sparky42  Offline OP
New Member
Joined: Jun 2016
Posts: 2
CA
Hmmm, the breaker box is mounted on a metal building. Can I consider the breaker box as the source location? In that case there is a ground wire connected to the breaker box itself (and it comes out via the IEC-309 connector). This is not a permanent installation it will only be active for a month or so.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
248,675 Are you busy
186,419 Re: Forum
175,900 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 15 (0.004s) Memory: 0.9600 MB (Peak: 1.0916 MB) Zlib enabled. Server Time: 2018-08-21 15:44:24 UTC