Outdoor transformer/grounding question #217353 06/23/16 02:10 AM
Joined: Jun 2016
Posts: 2
S
Sparky42 Offline OP
New Member
Application is an outdoor 30kVA, 480V/400V step down delta-wye transformer to be located within 10 feet of a building panel breaker box. The box has three phase 480V fused power and an input ground wire tied to the breaker box via a screw lug. The output is a 3P4W IEC-309 receptacle, the ground pin of the receptacle has a wire that screws into the breaker box. My question is: Can I use the receptacle ground wire to be the ground for the transformer chassis and X0 of the secondary (via a terminal bar inside and bonded to the transformer enclosure)? Or will I have to run a ground wire independent of the receptacle so that ground is always made regardless of if the plug is in the receptacle. I could not find this detail in NEC.

2017 / 2014 NEC & Related Books and Study Guides
Re: Outdoor transformer/grounding question [Re: Sparky42] #217354 06/23/16 03:20 AM
Joined: Jul 2004
Posts: 9,577
G
gfretwell Offline
Member
I suppose you need to back up and see if that transformer is listed for cord and plug connection. If that is OK, I suppose the pin in the plug is sufficient to establish the ground.
Those 309 plugs are designed so the ground makes before the ungrounded pins.


Greg Fretwell
Re: Outdoor transformer/grounding question [Re: Sparky42] #217387 07/01/16 12:59 AM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline
Member
Read 2014 N.E.C. 250.30 (C)

Re: Outdoor transformer/grounding question [Re: Sparky42] #217393 07/05/16 12:09 AM
Joined: Jun 2016
Posts: 2
S
Sparky42 Offline OP
New Member
Hmmm, the breaker box is mounted on a metal building. Can I consider the breaker box as the source location? In that case there is a ground wire connected to the breaker box itself (and it comes out via the IEC-309 connector). This is not a permanent installation it will only be active for a month or so.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 11
Popular Topics(Views)
277,998 Are you busy
211,432 Re: Forum
198,482 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3