Posted By: Sparky42 Outdoor transformer/grounding question - 06/23/16 06:10 AM
Application is an outdoor 30kVA, 480V/400V step down delta-wye transformer to be located within 10 feet of a building panel breaker box. The box has three phase 480V fused power and an input ground wire tied to the breaker box via a screw lug. The output is a 3P4W IEC-309 receptacle, the ground pin of the receptacle has a wire that screws into the breaker box. My question is: Can I use the receptacle ground wire to be the ground for the transformer chassis and X0 of the secondary (via a terminal bar inside and bonded to the transformer enclosure)? Or will I have to run a ground wire independent of the receptacle so that ground is always made regardless of if the plug is in the receptacle. I could not find this detail in NEC.
Posted By: gfretwell Re: Outdoor transformer/grounding question - 06/23/16 07:20 AM
I suppose you need to back up and see if that transformer is listed for cord and plug connection. If that is OK, I suppose the pin in the plug is sufficient to establish the ground.
Those 309 plugs are designed so the ground makes before the ungrounded pins.
Posted By: Yoopersup Re: Outdoor transformer/grounding question - 07/01/16 04:59 AM
Read 2014 N.E.C. 250.30 (C)
Posted By: Sparky42 Re: Outdoor transformer/grounding question - 07/05/16 04:09 AM
Hmmm, the breaker box is mounted on a metal building. Can I consider the breaker box as the source location? In that case there is a ground wire connected to the breaker box itself (and it comes out via the IEC-309 connector). This is not a permanent installation it will only be active for a month or so.