Working space in front of elevated busduct system
#217136
05/13/16 06:44 PM
|
Joined: Jul 2004
Posts: 783
OP
Member
|
Existing warehouse. 2000A service feeding busduct hung off of outside wall. Busduct is 12 feet above floor. All connections from disconnects go up. Owner wants to put workbenches and tool storage cabinets no taller than six feet, below bus, along the wall.
Electrician says no, need to maintain working clearance. I thought the only requirements were 36 inches in front of, six feet or hard ceiling above, and four feet below bottom of disconnect.
Am I completely off base?
Thanks
|
|
|
Re: Working space in front of elevated busduct system
[Re: LarryC]
#217148
05/16/16 07:05 AM
|
Joined: May 2005
Posts: 984
Member
|
I think the Electrician is correct. How would you access the bus without moving the cabinets?
Ghost307
|
|
|
Re: Working space in front of elevated busduct system
[Re: LarryC]
#217151
05/16/16 11:57 AM
|
Joined: Jul 2004
Posts: 9,571
Member
|
What is in the bus duct? Is it something that is "likely to require examination, adjustment, servicing, or maintenance while energized"?
Can they simply put a catwalk over the cabinets? They are 12' AFF. What is the access now?
Greg Fretwell
|
|
|
Re: Working space in front of elevated busduct system
[Re: gfretwell]
#217152
05/16/16 04:58 PM
|
Joined: Jul 2004
Posts: 783
OP
Member
|
Is it something that is "likely to require examination, adjustment, servicing, or maintenance while energized"? That was my point. If you have to move or add a disconnect, then move the benches or cabinets at that time. Otherwise the only expected operation while energized would be operating the disconnect via an insulated pole. Fuse replacement would be done after operating the disconnect and access to the disconnect is easily arranged by step ladder or manlift.
|
|
|
|
|