Joined: Jul 2004
Posts: 787
L
LarryC Offline OP
Member
Existing warehouse. 2000A service feeding busduct hung off of outside wall. Busduct is 12 feet above floor. All connections from disconnects go up. Owner wants to put workbenches and tool storage cabinets no taller than six feet, below bus, along the wall.

Electrician says no, need to maintain working clearance. I thought the only requirements were 36 inches in front of, six feet or hard ceiling above, and four feet below bottom of disconnect.

Am I completely off base?

Thanks

Joined: May 2005
Posts: 984
Likes: 1
G
Member
I think the Electrician is correct.
How would you access the bus without moving the cabinets?


Ghost307
Joined: Jul 2004
Posts: 9,788
Likes: 14
G
Member
What is in the bus duct? Is it something that is "likely to require examination, adjustment, servicing, or maintenance while energized"?

Can they simply put a catwalk over the cabinets? They are 12' AFF. What is the access now?


Greg Fretwell
Joined: Jul 2004
Posts: 787
L
LarryC Offline OP
Member
Quote
Is it something that is "likely to require examination, adjustment, servicing, or maintenance while energized"?


That was my point. If you have to move or add a disconnect, then move the benches or cabinets at that time. Otherwise the only expected operation while energized would be operating the disconnect via an insulated pole.

Fuse replacement would be done after operating the disconnect and access to the disconnect is easily arranged by step ladder or manlift.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Top Posters(30 Days)
BigB 9
triple 3
Popular Topics(Views)
302,487 Are you busy
231,878 Re: Forum
216,501 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5