Hid lights on GFCI breaker #217102 05/03/16 09:07 PM
Joined: Jul 2007
Posts: 265
W
wire_twister Offline OP
Member
Hello everyone, been lurking for a while, now have a question. Has anyone had any success running HID lights, specificaly HPS light fixtures on a GFCI breaker? Put power to a boat dock, installed 2 HPS fixtures, and cannot get the breaker to reset. These are new fixtures, and will function normally when plugged in on a non GFCI circuit. I can un-hook the neutral wire going to these fixtures and the breaker will reset, allowing the rest of the things on the circuit to function normally. Only thing I can figure is a neutral to ground bond in the ballast causing the breaker to trip. Does anyone know of a manufacturer that has lights that will work on these circuits? The fixtures in question are made by Lithonia. Any insight would be appreciated.


Jimmy

Life is tough, Life is tougher when you are stupid
Work Gear for Electricians and the Trades
Re: Hid lights on GFCI breaker [Re: wire_twister] #217105 05/04/16 08:46 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
Simply operating an HID light on a circuit protected by a GFCI should not be a problem. However ...

Ballasts (and HID fixtures have ballasts) often fault to ground. That will trip the GFCI. The solution is to replace the ballast.

As for breakers marked "HID," here is what UL has to say: "A circuit breaker rated 50 A maximum, 480 V or less, and intended to switch high
intensity discharge (HID) lighting loads on a regular basis is marked “HID.” "


Re: Hid lights on GFCI breaker [Re: wire_twister] #217106 05/04/16 09:35 PM
Joined: Jul 2007
Posts: 265
W
wire_twister Offline OP
Member
Reno,
The fixtures are new, I took them out of the box, hard for me to believe both ballasts are bad. Could it be a manufacturing problem. Both will work on a non-gfci circuit.


Jimmy

Life is tough, Life is tougher when you are stupid
Re: Hid lights on GFCI breaker [Re: wire_twister] #217107 05/05/16 04:08 PM
Joined: Apr 2002
Posts: 7,150
HotLine1 Offline
Member
Jimmy:
1: Are the ballasts multi-tap (120-240V)??
2: Can you make the circuit 240 volt??
3: Are the fixtures and wiring 'out of reach'??



John
Re: Hid lights on GFCI breaker [Re: wire_twister] #217109 05/05/16 07:34 PM
Joined: Jul 2007
Posts: 265
W
wire_twister Offline OP
Member
John,
They are not multi tap, but they are out of reach. Thought about putting them on a non Gfci circuit, but worried about some one tapping it for other uses.


Jimmy

Life is tough, Life is tougher when you are stupid
Re: Hid lights on GFCI breaker [Re: wire_twister] #217111 05/05/16 10:09 PM
Joined: Apr 2002
Posts: 7,150
HotLine1 Offline
Member
Jimmy;

Yes, I know it's tough to idiot proof your work once you are gone.

I thought that most of the new fixtures came with multi-volt ballasts, but you just killed that.

Just a thought, did you try the circuit with the ballast ground conductor disconnected? If it still trips, and the ballast is leaking to ground, then you could try putting fiber/plastic washers to isolate the ballast case from the fixture body. (Internal leakage to ground). Keep the fixture body bonded at all times. You could then contact Lithonia to determine if they will replace the ballasts.

Just a thought...




John
Re: Hid lights on GFCI breaker [Re: wire_twister] #217113 05/06/16 08:58 AM
Joined: Jul 2007
Posts: 265
W
wire_twister Offline OP
Member
I will check that, thanks for the insight John.


Jimmy

Life is tough, Life is tougher when you are stupid
Re: Hid lights on GFCI breaker [Re: wire_twister] #217123 05/10/16 06:49 PM
Joined: Jul 2007
Posts: 265
W
wire_twister Offline OP
Member
update: I went with Johns advice, and used some rubber to isolate the ballast from the fixture housing, and bingo, the breaker will reset and hold. Took the rubber out just to verify and the breaker will not set. Waiting on an answer from Lithonia to see if they are going to replace them or just ignore the problem. I could not see a bond from neutral to ground, nor could I read any leakage with my Fluke meter, but the proof is in the pudding. I will bet Lithonia knows the problem exists just havent had enough complaints to do anything about it yet. HID lighting on docks for fish attractant is just starting to catch on in my area, bet there will be more trouble to come.


Jimmy

Life is tough, Life is tougher when you are stupid
Re: Hid lights on GFCI breaker [Re: wire_twister] #217126 05/10/16 10:08 PM
Joined: Apr 2002
Posts: 7,150
HotLine1 Offline
Member
Jimmy:

If you don't get anywhere with the mfg., you did find a "fix". IF you have a ballast 'in stock' you may want to swap it out to see IF that is the 100% cure.

Perhaps Greg has some input on ballast leakage to ground?

I can say I never came upon this issue in my 'tool days', and the majority of the HID lighting I worked on was 208 to 480 volt.



John
Re: Hid lights on GFCI breaker [Re: wire_twister] #217127 05/11/16 04:23 AM
Joined: Jul 2004
Posts: 9,452
G
gfretwell Offline
Member
I suppose the first thing would be to see if it is the hot or neutral leaking (what voltage do you measure from the floating ballast to ground?) but it really doesn't matter. Both represent a potential hazard.
I am curious what the mfg says.

It is possible that this is just the RF filter providing a fault path. That used to be a problem on some old computer power supplies until U/L tightened up the listing standard.


Greg Fretwell
Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,720
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 12
Admin 8
Popular Topics(Views)
264,436 Are you busy
199,267 Re: Forum
188,382 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3