Table 39 #217072
04/22/16 09:42 PM
04/22/16 09:42 PM
B
brsele  Offline OP
Member
Joined: Jul 2008
Posts: 98
Northern Ontario
So Ontario is adopting the new code starting May 1st.
As I believe most of you have been working with the new code for a year now, I have a question with regards to the new table 39.

As per 8-104(6)(a), when would somebody put an 89A calculated load on a 100A service?

Or is somebody manufacturing main breakers now rated for 100%

Thanks... Bruce

Tools for Electricians:
Re: Table 39 [Re: brsele] #217073
04/23/16 05:35 PM
04/23/16 05:35 PM
T
twh  Offline
Member
Joined: Mar 2004
Posts: 947
Regina, Sask.
8-200(3) says calculated loads for residential services are not continuous.

Re: Table 39 [Re: brsele] #217074
04/23/16 09:03 PM
04/23/16 09:03 PM
B
brsele  Offline OP
Member
Joined: Jul 2008
Posts: 98
Northern Ontario
Thanks TWH.
This question came to me as I've been asked to wire a new house being built with electric heat. A 100A service was specified.

This is the first time in my life I've been asked to supply a 100A service for a new house and electric baseboard heaters.

So I did a load calculation and came up with 85A.

I always thought that the max. calculated load for a 100A service was 80A and the max. for 200A was 160A.

I'm wondering if this is a case where I was originally taught wrong and never questioned it, or if something changed and I never noticed because everybody asks for a 200A service.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,905
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,445 Are you busy
190,685 Re: Forum
180,402 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 15 (0.005s) Memory: 0.9507 MB (Peak: 1.0769 MB) Zlib enabled. Server Time: 2019-04-19 10:50:24 UTC