#216753 - 02/11/16 08:13 PM Kitchen AFCIs  
sparkync  Offline
Member
Joined: Oct 2002
Posts: 819
NC
Could someone refresh my memory on the use of AFCIs in the kitchen? GFCIs are still required around the counter, but code says that kitchens require AFCI's too. How's this accomplished? A combination device?
Thanks..


2017 / 2014 NEC & Related Books and Study Guides

#216755 - 02/11/16 09:40 PM Re: Kitchen AFCIs [Re: sparkync]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Personally, I'd either use an AFCI breaker with a GFCI device downstream, or an AFCI device feeding a GFCI device.


#216759 - 02/12/16 02:34 AM Re: Kitchen AFCIs [Re: sparkync]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,080
Estero,Fl,usa
Cuttler Hammer does sell a GFCI/AFCI combo breaker but I agree with Reno. Trouble shooting is easier if you have a GFCI device at the counter top.
I really had to look this one up because we are still on the 11 here and that is a 14 requirement. I was thinking the kitchen was exempt. Silly me.


Greg Fretwell

#216764 - 02/14/16 01:54 PM Re: Kitchen AFCIs [Re: sparkync]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,826
Brick, NJ USA
Just something to make you guys laugh....

Final on a resi addition, panel had 3-GFI CBs, no AFCI CBs.
H/O said.."I know he put them in, I paid extra".

Went to kitchen.....wow, the elusive AFCI devices!! And, they were not on the GFI CBs!!

BTW, this job was not DIY, it has a EC!!




John

#216776 - 02/17/16 01:52 AM Re: Kitchen AFCIs [Re: HotLine1]  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,308
Rumour is 210.12's requirements will be all 120V circuitry in the '17 , and 210.8's 'readily accessible GFCI' is making DP (dual purpose) breakers much more appealing, considering the 'gfci under the sink for the pig/dish' debate.....

Myself, a DP 50A spa disco setup ahead of an MLO panel kitchen subpanel may be a consideration .....

~S~




Member Spotlight
Niko
Niko
Campbell, CA
Posts: 356
Joined: August 2006
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 15 (0.002s) Memory: 0.7696 MB (Peak: 0.9094 MB) Zlib enabled. Server Time: 2017-05-30 12:53:47 UTC