steel bushings #215142
03/08/15 05:19 PM
03/08/15 05:19 PM
T
triple  Offline OP
Member
Joined: Apr 2002
Posts: 184
Wisconsin
Are steel bushings allowed on rigid pipe terminations for conductors #4 or larger? 300.4(G) appears to say no. When used on smaller conductors, is the steel bushing listed for use without a locknut inside the box?

2017 / 2014 NEC & Related Books and Study Guides
Re: steel bushings [Re: triple] #215143
03/08/15 05:41 PM
03/08/15 05:41 PM
T
triple  Offline OP
Member
Joined: Apr 2002
Posts: 184
Wisconsin
Also, even though it is not stated in 352.46, I would assume steel bushing would not be allowed on PVC due to a lack of connection to ground. And to be clear, I am refurring to standard/non bond bushings in these post. The Handbook shows bond bushings being used without locknuts so it is probably safe to assume that doesn't violate their UL Listing.

Re: steel bushings [Re: triple] #215144
03/08/15 06:53 PM
03/08/15 06:53 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,279
Fullerton, CA USA
Sure they're allowed ..... as long as they have an insulated throat.

[Linked Image]

Re: steel bushings [Re: triple] #215149
03/10/15 07:46 PM
03/10/15 07:46 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Where is it written that they must have plastic throats?

The current Steel City catalog shoes several styles of metal bushings. Some are zinc and some are iron. Several do not have any sort of liner. All show a current UL listing.

Or ... are these another 'forbidden fitting" to add to the other thread?

Re: steel bushings [Re: triple] #215152
03/11/15 08:19 AM
03/11/15 08:19 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,279
Fullerton, CA USA
300.4(G)
Insulated Fittings. Where raceways contain 4 AWG or larger insulated circuit conductors, and these conductors
enter a cabinet, a box, an enclosure, or a raceway, the conductors shall be protected by an identified fitting providing a smoothly rounded insulating surface, unless the conductors are separated from the fitting or raceway by identified insulating material that is securely fastened in place.


They could be listed if they're not intended to put conductors #4 or larger in the conduit.

Re: steel bushings [Re: triple] #215159
03/11/15 07:36 PM
03/11/15 07:36 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Well, that's enough to keep them from my 'illegal fittings' thread!

To be fair, I've only seen the metal bushings on 3/4 and 1/2 pipe. Not much room for big wires there! Plus, they've all been older jobs, quite possibly from the days before plastic.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
andey 3
Popular Topics(Views)
253,234 Are you busy
189,881 Re: Forum
179,584 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.024s Queries: 15 (0.004s) Memory: 0.9774 MB (Peak: 1.1265 MB) Zlib enabled. Server Time: 2019-02-18 13:08:19 UTC