steel bushings #215142 03/08/15 06:19 PM
Joined: Apr 2002
Posts: 184
T
triple Offline OP
Member
Are steel bushings allowed on rigid pipe terminations for conductors #4 or larger? 300.4(G) appears to say no. When used on smaller conductors, is the steel bushing listed for use without a locknut inside the box?

2017 / 2014 NEC & Related Books and Study Guides
Re: steel bushings [Re: triple] #215143 03/08/15 06:41 PM
Joined: Apr 2002
Posts: 184
T
triple Offline OP
Member
Also, even though it is not stated in 352.46, I would assume steel bushing would not be allowed on PVC due to a lack of connection to ground. And to be clear, I am refurring to standard/non bond bushings in these post. The Handbook shows bond bushings being used without locknuts so it is probably safe to assume that doesn't violate their UL Listing.

Re: steel bushings [Re: triple] #215144 03/08/15 07:53 PM
Joined: Dec 2000
Posts: 4,281
electure Offline
Member
Sure they're allowed ..... as long as they have an insulated throat.

[Linked Image]

Re: steel bushings [Re: triple] #215149 03/10/15 08:46 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
Where is it written that they must have plastic throats?

The current Steel City catalog shoes several styles of metal bushings. Some are zinc and some are iron. Several do not have any sort of liner. All show a current UL listing.

Or ... are these another 'forbidden fitting" to add to the other thread?

Re: steel bushings [Re: triple] #215152 03/11/15 09:19 AM
Joined: Dec 2000
Posts: 4,281
electure Offline
Member
300.4(G)
Insulated Fittings. Where raceways contain 4 AWG or larger insulated circuit conductors, and these conductors
enter a cabinet, a box, an enclosure, or a raceway, the conductors shall be protected by an identified fitting providing a smoothly rounded insulating surface, unless the conductors are separated from the fitting or raceway by identified insulating material that is securely fastened in place.


They could be listed if they're not intended to put conductors #4 or larger in the conduit.

Re: steel bushings [Re: triple] #215159 03/11/15 08:36 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
Well, that's enough to keep them from my 'illegal fittings' thread!

To be fair, I've only seen the metal bushings on 3/4 and 1/2 pipe. Not much room for big wires there! Plus, they've all been older jobs, quite possibly from the days before plastic.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 11
Popular Topics(Views)
258,501 Are you busy
194,117 Re: Forum
183,619 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3