Wall Mounted Oven 4.1KW #214757
01/21/15 01:59 PM
01/21/15 01:59 PM
SparksFlying  Offline OP
New Member
Joined: Oct 2014
Posts: 6
Austin, Texas
What size breaker and what size cable should be used.

Tools for Electricians:
Re: Wall Mounted Oven 4.1KW [Re: SparksFlying] #214758
01/21/15 05:48 PM
01/21/15 05:48 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,251
Estero,Fl,usa
Sounds like 10ga/30a to me. What do the instructions say?
A lot of times they say 8ga/40a no matter what oven is installed.


Greg Fretwell
Re: Wall Mounted Oven 4.1KW [Re: SparksFlying] #214786
01/24/15 01:24 PM
01/24/15 01:24 PM
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
4100 VA / 240V = 17.0833333- Amps

As Greg has mentioned, #8 THHN CU. protected by a 40 Amp 2 Pole Breaker is "The Norm".

--Scott (EE)


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Re: Wall Mounted Oven 4.1KW [Re: SparksFlying] #214791
01/24/15 03:45 PM
01/24/15 03:45 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,251
Estero,Fl,usa
It would probably live forever on 12ga and 20a breaker, even with the timer and the light inside but you should still be sizing at 125% of the calculated current. That is how I got to 10ga/30a.


Greg Fretwell
Re: Wall Mounted Oven 4.1KW [Re: SparksFlying] #214812
01/26/15 03:49 PM
01/26/15 03:49 PM
SparksFlying  Offline OP
New Member
Joined: Oct 2014
Posts: 6
Austin, Texas
Yes they only call for a 20ga and 20amp breaker but we are going with a 10ga/30amp and sleep well...'

Thanks


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
BigB 2
Popular Topics(Views)
248,562 Are you busy
186,276 Re: Forum
175,743 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 15 (0.004s) Memory: 0.9678 MB (Peak: 1.1092 MB) Zlib enabled. Server Time: 2018-08-16 21:33:47 UTC