What size breaker and what size cable should be used.
|
|
|
Re: Wall Mounted Oven 4.1KW
[Re: SparksFlying]
#214758
01/21/15 04:48 PM
|
Joined: Jul 2004
Posts: 9,559
Member
|
Sounds like 10ga/30a to me. What do the instructions say? A lot of times they say 8ga/40a no matter what oven is installed.
Greg Fretwell
|
|
|
Re: Wall Mounted Oven 4.1KW
[Re: SparksFlying]
#214786
01/24/15 12:24 PM
|
Joined: Oct 2000
Posts: 2,721
Broom Pusher and Member
|
4100 VA / 240V = 17.0833333- Amps
As Greg has mentioned, #8 THHN CU. protected by a 40 Amp 2 Pole Breaker is "The Norm".
--Scott (EE)
Scott " 35 " Thompson Just Say NO To Green Eggs And Ham!
|
|
|
Re: Wall Mounted Oven 4.1KW
[Re: SparksFlying]
#214791
01/24/15 02:45 PM
|
Joined: Jul 2004
Posts: 9,559
Member
|
It would probably live forever on 12ga and 20a breaker, even with the timer and the light inside but you should still be sizing at 125% of the calculated current. That is how I got to 10ga/30a.
Greg Fretwell
|
|
|
Re: Wall Mounted Oven 4.1KW
[Re: SparksFlying]
#214812
01/26/15 02:49 PM
|
Joined: Oct 2014
Posts: 6
OP
New Member
|
Yes they only call for a 20ga and 20amp breaker but we are going with a 10ga/30amp and sleep well...'