ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Explored: Basics of PLC
by niamishra. 10/19/18 04:44 AM
Linear Power Supply Quits Under Load
by JoeTestingEngr. 10/18/18 08:47 PM
220/230/240V 60Hz Systems
by dsk. 10/17/18 01:25 PM
PLC/HMI Enclosure C2, D1
by ghost307. 10/16/18 03:31 PM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 6 guests, and 24 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Wall Mounted Oven 4.1KW #214757
01/21/15 01:59 PM
01/21/15 01:59 PM
SparksFlying  Offline OP
New Member
Joined: Oct 2014
Posts: 6
Austin, Texas
What size breaker and what size cable should be used.

Tools for Electricians:
Re: Wall Mounted Oven 4.1KW [Re: SparksFlying] #214758
01/21/15 05:48 PM
01/21/15 05:48 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
Sounds like 10ga/30a to me. What do the instructions say?
A lot of times they say 8ga/40a no matter what oven is installed.


Greg Fretwell
Re: Wall Mounted Oven 4.1KW [Re: SparksFlying] #214786
01/24/15 01:24 PM
01/24/15 01:24 PM
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
4100 VA / 240V = 17.0833333- Amps

As Greg has mentioned, #8 THHN CU. protected by a 40 Amp 2 Pole Breaker is "The Norm".

--Scott (EE)


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Re: Wall Mounted Oven 4.1KW [Re: SparksFlying] #214791
01/24/15 03:45 PM
01/24/15 03:45 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
It would probably live forever on 12ga and 20a breaker, even with the timer and the light inside but you should still be sizing at 125% of the calculated current. That is how I got to 10ga/30a.


Greg Fretwell
Re: Wall Mounted Oven 4.1KW [Re: SparksFlying] #214812
01/26/15 03:49 PM
01/26/15 03:49 PM
SparksFlying  Offline OP
New Member
Joined: Oct 2014
Posts: 6
Austin, Texas
Yes they only call for a 20ga and 20amp breaker but we are going with a 10ga/30amp and sleep well...'

Thanks


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
richard
richard
L.I. New York
Posts: 98
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,500 Are you busy
188,059 Re: Forum
177,698 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 15 (0.004s) Memory: 0.9681 MB (Peak: 1.1097 MB) Zlib enabled. Server Time: 2018-10-20 15:07:25 UTC