ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
Why cables look like they do
by LongRunner. 04/26/17 09:36 AM
Dimmable LED 2x4 lay in fixtures
by HotLine1. 04/24/17 05:43 PM
Old decora style outlets
by Lostazhell. 04/22/17 07:59 PM
Permit Snafus...AHJs and Contractors Jump in
by gfretwell. 04/22/17 01:11 PM
How do you find a good employee?
by HotLine1. 04/22/17 10:44 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
234,813 Are you busy
169,590 Re: Forum
162,842 Need opinion
Who's Online Now
0 registered members (), 102 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#214757 - 01/21/15 01:59 PM Wall Mounted Oven 4.1KW  
SparksFlying  Offline
New Member
Joined: Oct 2014
Posts: 6
Austin, Texas
What size breaker and what size cable should be used.


Tools for Electricians:

#214758 - 01/21/15 05:48 PM Re: Wall Mounted Oven 4.1KW [Re: SparksFlying]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,069
Estero,Fl,usa
Sounds like 10ga/30a to me. What do the instructions say?
A lot of times they say 8ga/40a no matter what oven is installed.


Greg Fretwell

#214786 - 01/24/15 01:24 PM Re: Wall Mounted Oven 4.1KW [Re: SparksFlying]  
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,707
Anaheim, CA. USA
4100 VA / 240V = 17.0833333- Amps

As Greg has mentioned, #8 THHN CU. protected by a 40 Amp 2 Pole Breaker is "The Norm".

--Scott (EE)


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

#214791 - 01/24/15 03:45 PM Re: Wall Mounted Oven 4.1KW [Re: SparksFlying]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,069
Estero,Fl,usa
It would probably live forever on 12ga and 20a breaker, even with the timer and the light inside but you should still be sizing at 125% of the calculated current. That is how I got to 10ga/30a.


Greg Fretwell

#214812 - 01/26/15 03:49 PM Re: Wall Mounted Oven 4.1KW [Re: SparksFlying]  
SparksFlying  Offline
New Member
Joined: Oct 2014
Posts: 6
Austin, Texas
Yes they only call for a 20ga and 20amp breaker but we are going with a 10ga/30amp and sleep well...'

Thanks



Member Spotlight
Theelectrikid
Theelectrikid
Levittown, PA
Posts: 810
Joined: April 2004
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 15 (0.002s) Memory: 0.7687 MB (Peak: 0.9100 MB) Zlib enabled. Server Time: 2017-04-27 16:48:38 UTC