#214531 12/18/14 11:28 PM
Joined: Mar 2004
Posts: 785
B
BigB Offline OP
Member
When derating THWN-2 copper conductors for ambient that will eventually terminate in a sub panel with a 125 amp rating can I use the 90C column?

2017 / 2014 NEC & Related Books and Study Guides
Joined: Jun 2004
Posts: 1,273
T
Member
The sole and only reason for that column IS derating.

For there are no 90 degree rated devices out there.

One then uses the lesser computed ampacity limit.

So, yes, you start with the 90 degree column.


Tesla

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
pcsailor
pcsailor
Minneapolis, MN, USA
Posts: 21
Joined: September 2019
Top Posters(30 Days)
dsk 7
wa2ise 1
Popular Topics(Views)
284,930 Are you busy
217,466 Re: Forum
203,765 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5