derating rooftop conductors #214531 12/18/14 11:28 PM
Joined: Mar 2004
Posts: 765
B
BigB Offline OP
Member
When derating THWN-2 copper conductors for ambient that will eventually terminate in a sub panel with a 125 amp rating can I use the 90C column?

2017 / 2014 NEC & Related Books and Study Guides
Re: derating rooftop conductors [Re: BigB] #214533 12/19/14 04:54 AM
Joined: Jun 2004
Posts: 1,273
T
Tesla Offline
Member
The sole and only reason for that column IS derating.

For there are no 90 degree rated devices out there.

One then uses the lesser computed ampacity limit.

So, yes, you start with the 90 degree column.


Tesla

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
pcsailor
pcsailor
Minneapolis, MN, USA
Posts: 21
Joined: September 2019
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 8
Popular Topics(Views)
266,169 Are you busy
201,007 Re: Forum
189,696 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3