#214327 11/16/14 01:45 PM
Joined: Jan 2004
Posts: 1,507
G
Member
The question came to me about how far must the NM cable sheath enter the boxes? I could only find the information located in 334.15(C). Nothing about entering the box sans the conduit. My answer would be, the sheath must extend beyond the clamping device be it a non-metallic box or a metal one. The person calling me was concerned because his boss wants the sheath to be at least 3/4" into the box.
There's got to be more important things than this dispute.


George Little
Horizontal Ad
Joined: Apr 2002
Posts: 7,408
Likes: 7
Member
George:
From 314.17 (C) of 2014 NEC.....

Where nonmetallic sheathed cable or multi-conductor Type UF cable is used, the sheath shall extend not less than 6 mm (1/4 in.) inside the box and beyond any cable clamp. In all instances, all permitted wiring methods shall be secured to the boxes.


Last edited by HotLine1; 11/17/14 10:04 AM. Reason: Corrected copy booboo

John
Joined: Jul 2004
Posts: 10,002
Likes: 35
G
Member
1/4" in english


Greg Fretwell
Joined: May 2005
Posts: 984
Likes: 1
G
Member
Yep, 1/4" minimum.


Ghost307
Joined: Jan 2004
Posts: 1,507
G
Member
Thanks Guys. You are the best. I would have expected it to be in Article 334 but it wasn't. HEY Inspectors have every right to be wrong :)) And I'm probably one of the few that would admit it.

That's what this BB is all about.


George Little
Joined: Apr 2002
Posts: 7,408
Likes: 7
Member
George:
As I say to some..."I'm human, I do make mistakes too"


John
Joined: Jul 2004
Posts: 10,002
Likes: 35
G
Member
I guess it is because there is more than one kind of cable and they were trying to avoid the mess that was created when they put a cable rule in 320 and referred to it in all the other cable articles. (like accessible attics in 330.23 334.23 etc)


Greg Fretwell
Horizontal Ad

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Top Posters(30 Days)
Popular Topics(Views)
333,593 Are you busy
258,964 Re: Forum
240,394 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5