#213180 03/27/14 08:43 PM
Joined: Mar 2005
Posts: 240
Member
I went to look at a job, where some copper thieves stole the parking lot light control wires, from a church none the less.
I discovered the ground wire pulled with the home run is bare copper, which I thought was against code in a raceway. Am I right? Or was this another myth I believed in? Also what do you think about split bolting the 3 control wires and heat shrinking them in each hand hole? $50 a pop for the resin kits seems kinda pricing, when split bolts/heat shrink work just fine.

Thanks, H20

Last edited by watersparkfalls; 03/27/14 08:45 PM.
Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Jun 2004
Posts: 1,273
T
Member
I don't work the traffic and signals market...

But the last NEC/ IBEW job I saw used bare #10 solid as the grounding conductor inside PVC for street illumination. It appeared that they used 1 1/4" as their minimum conduit size.

I was kind of jealous, they had an entire 20-foot double axle trailer dedicated to holding their conductor selections. I could never get such a rig to roll around our big box slabs.

That's the only contractor I can recall using bare grounding conductors -- excluding bare solid grounding electrode conductors.


Tesla
Joined: Jul 2004
Posts: 9,689
Likes: 10
G
Member
The only restriction I know that might affect that is that 8ga or larger solid is not allowed in a raceway.
The only exception I can think of is a GEC.

Quote
310.3 Stranded Conductors.
Where installed in raceways, conductors of size 8 AWG and larger shall be stranded.
Exception: As permitted or required elsewhere in this Code.


Greg Fretwell
Joined: Apr 2002
Posts: 7,297
Likes: 6
Member
H2o:
No issue with the bare to my knowledge as Greg said.

Now, the split bolt issue. Do you mean 3 control conductors, or you have to put 3 into a split bolt?
Most, if not all split bolts are only listed/labeled (your choice) for two (2) conductors. ie; run/tap. Your AHJ may have an issue with 3 conductors.





John
Joined: Mar 2005
Posts: 240
Member
HotLine I was going to put all 3 control wires in the split bolt, NSI industries claim to have a listed split bolt for 3 copper wires. However I am leaning towards Ideals blue weatherproof wirenuts, they are rated for wet locations and my connections are in a hand hole, so might truly be the safest and cost effective way to reconnect lights. Need to secure hand holes from future thefts any thoughts on how to? Was thinking drilling and tapping, but that diamond plate is thick.

Not sure where I got it in my head "no bare in raceway" however I will double check my WAC(Washington Administrative Code)book, however if previous installer was signed off, must be fine.

Thanks,
H20

Joined: Apr 2002
Posts: 7,297
Likes: 6
Member
The Ideal big blues sound like a plan.


John
Joined: Jul 2007
Posts: 1,335
S
Member
Bare copper ground in a conduit is not a code issue spec issue perhaps but not a code issue.

As for the split bolts/resin question. That depends on the "engineer" of the project. If done right, split bolt/resin is definently bullet proof for a long tern installation. Way better then wire nuts given their location. If no rework or add to later is not in the cards, bullet proof is a definent plus if the customers are willing to pay for it.


"Live Awesome!" - Kevin Carosa

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Top Posters(30 Days)
Trumpy 5
LarryC 3
NORCAL 2
Popular Topics(Views)
291,501 Are you busy
223,930 Re: Forum
209,314 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5