Bare Copper In Raceway #213180
03/27/14 08:43 PM
03/27/14 08:43 PM
watersparkfalls  Offline OP
Member
Joined: Mar 2005
Posts: 222
Washington...Not DC
I went to look at a job, where some copper thieves stole the parking lot light control wires, from a church none the less.
I discovered the ground wire pulled with the home run is bare copper, which I thought was against code in a raceway. Am I right? Or was this another myth I believed in? Also what do you think about split bolting the 3 control wires and heat shrinking them in each hand hole? $50 a pop for the resin kits seems kinda pricing, when split bolts/heat shrink work just fine.

Thanks, H20

Last edited by watersparkfalls; 03/27/14 08:45 PM.
2017 / 2014 NEC & Related Books and Study Guides
Re: Bare Copper In Raceway [Re: watersparkfalls] #213181
03/27/14 09:47 PM
03/27/14 09:47 PM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
I don't work the traffic and signals market...

But the last NEC/ IBEW job I saw used bare #10 solid as the grounding conductor inside PVC for street illumination. It appeared that they used 1 1/4" as their minimum conduit size.

I was kind of jealous, they had an entire 20-foot double axle trailer dedicated to holding their conductor selections. I could never get such a rig to roll around our big box slabs.

That's the only contractor I can recall using bare grounding conductors -- excluding bare solid grounding electrode conductors.


Tesla
Re: Bare Copper In Raceway [Re: watersparkfalls] #213182
03/27/14 09:54 PM
03/27/14 09:54 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,222
Estero,Fl,usa
The only restriction I know that might affect that is that 8ga or larger solid is not allowed in a raceway.
The only exception I can think of is a GEC.

Quote
310.3 Stranded Conductors.
Where installed in raceways, conductors of size 8 AWG and larger shall be stranded.
Exception: As permitted or required elsewhere in this Code.


Greg Fretwell
Re: Bare Copper In Raceway [Re: watersparkfalls] #213185
03/28/14 10:54 AM
03/28/14 10:54 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,963
Brick, NJ USA
H2o:
No issue with the bare to my knowledge as Greg said.

Now, the split bolt issue. Do you mean 3 control conductors, or you have to put 3 into a split bolt?
Most, if not all split bolts are only listed/labeled (your choice) for two (2) conductors. ie; run/tap. Your AHJ may have an issue with 3 conductors.





John
Re: Bare Copper In Raceway [Re: watersparkfalls] #213190
03/28/14 03:19 PM
03/28/14 03:19 PM
watersparkfalls  Offline OP
Member
Joined: Mar 2005
Posts: 222
Washington...Not DC
HotLine I was going to put all 3 control wires in the split bolt, NSI industries claim to have a listed split bolt for 3 copper wires. However I am leaning towards Ideals blue weatherproof wirenuts, they are rated for wet locations and my connections are in a hand hole, so might truly be the safest and cost effective way to reconnect lights. Need to secure hand holes from future thefts any thoughts on how to? Was thinking drilling and tapping, but that diamond plate is thick.

Not sure where I got it in my head "no bare in raceway" however I will double check my WAC(Washington Administrative Code)book, however if previous installer was signed off, must be fine.

Thanks,
H20

Re: Bare Copper In Raceway [Re: watersparkfalls] #213191
03/28/14 03:50 PM
03/28/14 03:50 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,963
Brick, NJ USA
The Ideal big blues sound like a plan.


John
Re: Bare Copper In Raceway [Re: watersparkfalls] #213204
03/29/14 03:02 PM
03/29/14 03:02 PM
S
sparkyinak  Online Content
Member
Joined: Jul 2007
Posts: 1,332
Alaska
Bare copper ground in a conduit is not a code issue spec issue perhaps but not a code issue.

As for the split bolts/resin question. That depends on the "engineer" of the project. If done right, split bolt/resin is definently bullet proof for a long tern installation. Way better then wire nuts given their location. If no rework or add to later is not in the cards, bullet proof is a definent plus if the customers are willing to pay for it.


"Live Awesome!" - Kevin Carosa

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
twh 12
Popular Topics(Views)
246,845 Are you busy
184,205 Re: Forum
173,446 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.029s Queries: 15 (0.005s) Memory: 0.9868 MB (Peak: 1.1448 MB) Zlib enabled. Server Time: 2018-05-21 01:16:24 UTC