ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat Box
Recent Posts
Any Woodworkers here?
by gfretwell - 05/13/21 01:47 AM
Your favourite food?
by Bill Addiss - 05/12/21 05:23 PM
Lock-down Thread
by gfretwell - 05/11/21 12:30 PM
Do You Travel?
by gfretwell - 05/11/21 12:16 PM
Just be aware of this...
by gfretwell - 05/10/21 07:30 PM
New in the Gallery:
2020 - 2021 Winter Project
Garden 2021
Who's Online Now
1 registered members (HotLine1), 15 guests, and 13 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 4 1 2 3 4
Re: HVAC #211876 11/19/13 11:20 PM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline OP
Member
You are running a feed a 20 amp 240 volt feed to air air condition compressor outside. You decide to run a 12-3 RX wire and install a weatherproof GFI receptacle across the red and black wire of that 12- RX wire and use the black and red wire for the HVAC. The receptacle is wired in before the disconnect, so that you can De-energize the AC and still have the recpt. hot.

Does this meet code? Yes? No, if not, code sections please.


Last edited by harold endean; 11/19/13 11:21 PM.
Work Gear for Electricians and the Trades
Re: HVAC [Re: harold endean] #211879 11/20/13 12:19 AM
Joined: Mar 2004
Posts: 782
B
BigB Offline
Member
I think you meant to say the GFCI is wired between the red and white, or the black and white, not the red and black.

Anyways this is an interesting qquestion and I am going to be watching this one.

Last edited by BigB; 11/20/13 12:22 AM.
Re: HVAC [Re: harold endean] #211880 11/20/13 01:01 AM
Joined: Jul 2007
Posts: 265
W
wire_twister Offline
Member
I have contemplated doing this more than once, havent done it yet, too lazy to dig in the code for supporting articles. Like BigB said I will be watching this question.


Jimmy

Life is tough, Life is tougher when you are stupid
Re: HVAC [Re: harold endean] #211883 11/20/13 03:47 AM
Joined: Jul 2004
Posts: 9,623
G
gfretwell Online Content
Member
It certainly sounds like an interesting idea but I am going to sharpen my pencil and start looking at that condenser label.
You might get away with it if you had a small mini split with a 10a or less FLA. (210.23(A)(2) and 440.34)


Greg Fretwell
Re: HVAC [Re: harold endean] #211887 11/20/13 03:49 PM
Joined: Apr 2002
Posts: 7,261
HotLine1 Online Content
Member
Time to follow Greg & look thru the book. My gut is it could fly, as I can't put an Article on it right now.



John
Re: HVAC [Re: harold endean] #211895 11/20/13 09:33 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
Sure! Why not? (Though there might be other issues if you put 240 volts across a 120v GFCI :D)

Ultimately, you're describing a sort of tap - though no additional overcurrent protection is needed, as you're within the ratings of the conductors all the way.

Or, are you? Any condenser that calls for a maximum 20 amp breaker is also going to allow the use of #14 wire. You're also going to need a disconnect downstream, in addition to the breaker in the panel

Re: HVAC [Re: harold endean] #211896 11/20/13 09:37 PM
Joined: Nov 2005
Posts: 826
J
JoeTestingEngr Offline
Member
If it's not compliant, it should be. That sounds like the perfect service receptacle setup for maintenance.
Joe

Re: HVAC [Re: harold endean] #211899 11/21/13 03:04 AM
Joined: Sep 2002
Posts: 909
N
NORCAL Online Content
Member
There is 210.63, but it prohibits the required receptacle being connected to the LOAD side of the disconnecting means, this is from the 2008 NEC.

210.63 Heating, Air-Conditioning, and Refrigeration
Equipment Outlet. A 125-volt, single-phase, 15- or 20-
ampere-rated receptacle outlet shall be installed at an accessible
location for the servicing of heating, airconditioning,
and refrigeration equipment. The receptacle
shall be located on the same level and within 7.5 m (25 ft)
of the heating, air-conditioning, and refrigeration equipment.
The receptacle outlet shall not be connected to the
load side of the equipment disconnecting means.
Exception: A receptacle outlet shall not be required at oneand
two-family dwellings for the service of evaporative
coolers.

Re: HVAC [Re: harold endean] #211904 11/21/13 11:59 AM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
Technically it works, but if the AHJ asks if the 2-pole breaker is intended, and UL Listed, to protect a line-to-neutral load you may have a tough time answering.
About half of the time that I have seen this type of installation it has been passed, and gigged the other half.

Also 210.23(A)(2) prohibiting receptacles on a circuit feeding 'fixed in place' equipment would come into play.

Besides...if it were that easy why would they sell disconnect switches that have a GFCI already installed in them?
Go to www.geindustrial.com and search for DET-382 to see the GE product; several other manufacturers have the same thing.

IMHO I would suggest that you run this question by the AHJ to make sure that you won't have to tear anything out and do it over.


Ghost307
Re: HVAC [Re: harold endean] #211905 11/21/13 04:20 PM
Joined: Apr 2002
Posts: 7,261
HotLine1 Online Content
Member
Yes, 210.23 (A)(2) would work.

Thanks Ghost307


John
Page 1 of 4 1 2 3 4

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 7,261
Joined: April 2002
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 19
Admin 11
Popular Topics(Views)
278,914 Are you busy
212,073 Re: Forum
199,103 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3