E
Member
Can a GFCI receptacle be used as a disconnecting means for an out building (fed by only a single circuit) using the test button? I say no, but I saw this done over the weekend at a friend's place and he swears that it was inspected. I don't believe him.


---Ed---

"But the guy at Home Depot said it would work."
Horizontal Ad
Joined: Apr 2002
Posts: 7,401
Likes: 7
Member
IMHO, No!


John
Joined: Mar 2013
Posts: 46
Member
A GFCI CAN be used as a disconnecting means... that is what is supposed to do. This is not up for debate. Whether or not it is acceptable practice is the question.

A little more detail would be helpful, otherwise we'll be answering your question on a lot of assumptions.
There is a circuit, starting with a GFCI at the main building, which then runs to the out building?
Depending on the specific situation and the wiring in the outbuilding (the fact that it is only one circuit), I could see it being passed by an AHJ.

Last edited by NickD; 10/08/13 10:23 PM.
Joined: Jul 2007
Posts: 1,337
S
Member
GFCI's are not listed as a service disconnect thus can not be used as one


"Live Awesome!" - Kevin Carosa
Joined: Jul 2004
Posts: 9,993
Likes: 35
G
Member
The only exception to 225.38 is that a snap switch can be used in garages and out buildings on residential properties.
Nothing about a GFCI


Greg Fretwell
Joined: Apr 2002
Posts: 7,401
Likes: 7
Member
Again & IMHO no it cannot be a disconnect. Yes, in theory pushing the 'test' button will open the circuit, but it is not manufactured, designed or intended as a disconnect.


John
Joined: Jul 2004
Posts: 9,993
Likes: 35
G
Member
Sorry 225.36


Greg Fretwell
Horizontal Ad
Joined: Apr 2002
Posts: 7,401
Likes: 7
Member
Greg:
225.36 from 2011:
225.36 Suitable for Service Equipment. The disconnecting
means specified in 225.31 shall be suitable for use as
service equipment.
Exception: For garages and outbuildings on residential
property, a snap switch or a set of 3-way or 4-way snap
switches shall be permitted as the disconnecting means.

You are agreeing that a GFI cannot be used??


John
Joined: Jul 2004
Posts: 9,993
Likes: 35
G
Member
Yes. It is not a snap switch and it is not suitable as service equipment as AK sparky pointed out.


Greg Fretwell
Joined: Jul 2007
Posts: 1,337
S
Member
Test buttons don't always work on them


"Live Awesome!" - Kevin Carosa
Page 1 of 2 1 2

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
richard
richard
L.I. New York
Posts: 99
Joined: August 2003
Top Posters(30 Days)
BigB 6
Jam85 2
Popular Topics(Views)
329,731 Are you busy
254,598 Re: Forum
237,059 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5