Bonding Metal Piping 250.104 (B) #210276
06/07/13 12:47 PM
06/07/13 12:47 PM
akmaster  Offline OP
Member
Joined: Jun 2012
Posts: 70
alaska
Hi,
I am looking for the requirement for bonding the copper water lines to and from a hot water heater to the main disco, and the bonding required for gas lines..I also have sprinkler lines.

250.104 (B) seems to cover some of this but I recall my inspector making me bond to both copper lines from the water heater and then a bond to the gas meter piping..

thanks

greg


Don't drive and TEXT! Drive now TALK LATER!
2017 / 2014 NEC & Related Books and Study Guides
Re: Bonding Metal Piping 250.104 (B) [Re: akmaster] #210279
06/07/13 03:03 PM
06/07/13 03:03 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,228
Estero,Fl,usa
I have had this discussion many times and it has been pointed out, the code does not specifically require a bond around the water heater or any other non-conductive fixture.
You can get there with the word "systems" by saying all of the pipe in the system needs to be bonded using the jumpers defined in 250.104 but you still have guys arguing the other side.


Greg Fretwell
Re: Bonding Metal Piping 250.104 (B) [Re: akmaster] #210296
06/08/13 07:09 PM
06/08/13 07:09 PM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Greg,

We are having the big big fight again about bonding gas pipe or not bonding gas pipes here in NJ. The National Fuel Code (which is adopted here) states that the gas line must be bonded. I don't have the exact words nearby but, we are suppose to run a bonding conductor from the customer side of the gas line/meter to the grounding electrode of the electrical system. (The ground rods.)

Re: Bonding Metal Piping 250.104 (B) [Re: akmaster] #210303
06/09/13 02:32 AM
06/09/13 02:32 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,228
Estero,Fl,usa
I don't see much gas here. I am not sure what they are doing but I am for bonding everything metal.
I bonded my stainless counter top and the back splash.


Greg Fretwell
Re: Bonding Metal Piping 250.104 (B) [Re: gfretwell] #210305
06/09/13 08:50 AM
06/09/13 08:50 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,349
I hear some interesting theories on bonding

The main thing is, not every groundING conductor goes without passing some current

So you bond the gas pipes, and say they land the gas bottle (think rural area) in proximity to your meter & mbj

Methinks you fellas can visualize the circuit .....

~S~

Re: Bonding Metal Piping 250.104 (B) [Re: akmaster] #210310
06/09/13 12:14 PM
06/09/13 12:14 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,228
Estero,Fl,usa
Any piece of metal connected to the electrical system, intentionally or unintentionally, will carry some current.
There is no way to stop it.


Greg Fretwell
Re: Bonding Metal Piping 250.104 (B) [Re: akmaster] #210311
06/09/13 12:16 PM
06/09/13 12:16 PM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Sparky,

We had a problem with voltage getting on to gas piping several years ago in one of my towns. The gas co. was there to change out the meter and when the tech open up the gas pipe, there was a spark. The tech went nuts and blew the whistle. There were police, and fire dept. and utility people all around the area in minutes.

I think the problem was the neutral broke loose. There were no ground rods, the city water ground clamp was either bad, loose, or missing, so the ground was carrying the neutral load, right back on the gas piping system.

Re: Bonding Metal Piping 250.104 (B) [Re: akmaster] #210312
06/09/13 12:21 PM
06/09/13 12:21 PM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
There is discussions around this area with bonding of CSST piping. CSST is Corrugated Stainless Steel Pipe, it is that flex yellow pipe or trac (track) pipe which is black colored. Some people think it has to be bonded at the fittings and some don't. Some also think the bond wire should parallel the CSST and some say no it doesn't.

Re: Bonding Metal Piping 250.104 (B) [Re: gfretwell] #210314
06/09/13 01:46 PM
06/09/13 01:46 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,349
Quote
Any piece of metal connected to the electrical system, intentionally or unintentionally, will carry some current.
There is no way to stop it.



yeah i know Greg

the poco guys tell me the closer i am to a substation, the more i can expect it too....

~S~

Last edited by sparky; 06/09/13 01:47 PM.
Re: Bonding Metal Piping 250.104 (B) [Re: harold endean] #210315
06/09/13 01:48 PM
06/09/13 01:48 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,349
Originally Posted by harold endean
Sparky,

We had a problem with voltage getting on to gas piping several years ago in one of my towns. The gas co. was there to change out the meter and when the tech open up the gas pipe, there was a spark. The tech went nuts and blew the whistle. There were police, and fire dept. and utility people all around the area in minutes.



Oh great....

and i can just image them all pointing to me

"there he is!, git 'em "

~S~

Page 1 of 3 1 2 3

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
richard
richard
L.I. New York
Posts: 95
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
twh 5
Admin 2
Popular Topics(Views)
247,714 Are you busy
185,030 Re: Forum
174,362 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.035s Queries: 16 (0.006s) Memory: 1.0275 MB (Peak: 1.2100 MB) Zlib enabled. Server Time: 2018-06-25 07:32:20 UTC